ION 7550 - change the unit of energy delivered value

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7550 - change the unit of energy delivered value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
521
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
134
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2013-07-16 06:55 PM

0 Likes
11
3553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-16 06:55 PM

ION 7550 - change the unit of energy delivered value

Hi Everyone,

For ION7550, the default unit of energy delivered value is kWh, so it can not display the energy delivered value greater than 999 999 999 kWh (or 9 digits).

Attached file below is a real case of this issue, the actual value is 12 407 889,75 kWh, but the value displaying on ION7550 only 2 407 889,75 kWh.
1930

Can we change the unit of Energy Delivered value (displaying on the screen ION 7550) from kWh to MWh?

Thanks for your advice.

Regards,

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jimbradley
jimbradley Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-07-19 01:02 PM

0 Likes
2
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-19 01:02 PM

Hi Khanh,

I've attached a document that has the step by step instructions on how to do the changes you want using ION Setup.

There are a lot of steps but once you have done it once it should not take a lot of time.

Let me know if this works for you or if you have any questions.


Jim


See Answer In Context

Attachments
Reply
Replies 11
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2013-07-17 12:33 AM

0 Likes
1
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-17 12:33 AM

I believe if your CT size is high enough, it will automatically do this. I don't know what the exact numbers are, but it will change from kW to MW and current from A to kA

Reply
jimbradley
jimbradley Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-07-17 09:24 AM

0 Likes
6
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-17 09:24 AM

There are a number of ways to do this, all involve ION programming. 

Probably the simplest example would be to link the output of the kWh del integrator module into an new arithmetic module.  Divide the input by 1000 and label the result output register MWh del.   Link the MWh del  to the correct input of the "energy" screen.  For consistency I would do the same for kVArh del and kVAh del. 

Jim

Reply
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2013-07-17 06:55 PM

0 Likes
0
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-17 06:55 PM

Hi James,

Current setting on the meter: CT = 10.000 / 1A, PT = 20.000 / 110V

I checked with TSC L2, they just confirmed that the ION 7550 does not has automaticcaly scale function for energy value, we have to do ION programming to convert from kWh to MWh.

Thanks.

Reply
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2013-07-17 06:58 PM

0 Likes
5
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-17 06:58 PM

Hi Jim Bradley,

Did you test the ION programming for such requests? can you share me how to do as detail as possible?

Thanks,

Reply
jimbradley
jimbradley Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-07-18 08:46 AM

0 Likes
4
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-18 08:46 AM

Hi Khanh,

Are you familiar with ION Modules and frameworks etc ? Do you have any experience with the Designer program of PME?  Or do you have any experience with ION Setup?  I can provide a either a design file for Designer and instructions for Designer or instructions for how to do this with ION Setup.

Since ION programming is for functional configuration testing of small changes is up to the Application Engineer and generally is not done by a formal test department.

The best analogy I have is :

Meter Real Time OS  = PC BIOS

Meter Firmware = Windows  Note that the default frameworks are fully and formally tested. 

Meter ION programming = Application like Excel.

Jim

Reply
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2013-07-18 06:10 PM

0 Likes
3
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-18 06:10 PM

Hi Jim,

Yes, we're familiar with ION Setup & some experience with Designer program of PME.

If you have a real Designer program or ION setup for this case then please share with us, to help us not to waste time to study again.

Regards,

Reply
jimbradley
jimbradley Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-07-19 01:02 PM

0 Likes
2
3405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-19 01:02 PM

Hi Khanh,

I've attached a document that has the step by step instructions on how to do the changes you want using ION Setup.

There are a lot of steps but once you have done it once it should not take a lot of time.

Let me know if this works for you or if you have any questions.


Jim


Attachments
Reply
Matt_Curry
Administrator Matt_Curry Administrator
Administrator

Posted: ‎2013-07-19 02:12 PM

0 Likes
0
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-19 02:12 PM

Just moving this to the newly created Power Monitoring Hardware Community.

Reply
sesa149897_brid
Lieutenant JG sesa149897_brid Lieutenant JG
Lieutenant JG

Posted: ‎2013-07-21 11:26 PM

0 Likes
0
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-07-21 11:26 PM

Hi Jim,

Thanks a lot for your detail & useful instruction file, the meter now displaying MWh del value after modified ION programming.

Regards,

Reply
sesa261355
sesa261355 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-08-29 05:27 AM

0 Likes
1
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-08-29 05:27 AM

the following task of conversion of energy values to mega is being considered by a lot of customers. however as per the attached document, the conversion is all fine. however if the customer requires rollover count as well.this will not suit the purpose, as the energy value is in kilo , and as soon as it reaches the maximum value, the value will rollover back to zero. what is the solution in this scenario??

Reply
jimbradley
jimbradley Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-08-29 09:13 AM

1 Like
0
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-08-29 09:13 AM

Hi,

The solution is similar but things are done in a different order.  First link the real time power value, kW tot into a new arithmetic module.  Note that the there are 2 registers called kW tot, one from the Power Meter Module and one from an Arithmetic Module labeled "Scaling". To do the calculation the same as the default use the register from the Scaling Arithmetic module.  In the new Arithmetic module divide kW tot by 1000 and label the output register MW tot.  Create a new integrator module and link MW tot to the "Integrand" input of the Integrator module.  The other inputs , enable and reset, should be linked to same outputs as all the default Integrator Modules for consistency but this is not needed for the new Integrator Module to work.  Next set the new Integrator  Module setup register "RollValue" to the desired rollover point (in MHhr). Finally label the output register appropriately, e.g. MWhr del, and link it as required to display modules, data recorders etc.

Jim

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore