My customer electrical system installing IM400 & IFL12MC for Insulation Monitoring for application DC
I want know. Can i testing ( simulation) for testing fault current for IM400 & IFL12. Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @SESA528,
You can suggest testing this scenario by creating the fault close to the alarm threshold value of IFL12MC. For example, in IFL12MC, the nominal alarm threshold for 400VDC can be 40 kOhm, and the insulation fault test resistor value is 35 kOhm.
Link copied. Please paste this link to share this article on your social media post.
Hi team,
Pls help me. Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @SESA528,
You can suggest testing this scenario by creating the fault close to the alarm threshold value of IFL12MC. For example, in IFL12MC, the nominal alarm threshold for 400VDC can be 40 kOhm, and the insulation fault test resistor value is 35 kOhm.
Link copied. Please paste this link to share this article on your social media post.
Hi @Jesus_Diaz ,
Thanks very much. How about threshold kOhm for 220VDC?
Any IEC Standard mention to this Insulation Monitoring?