If they are connected, for example, like this, I would set CT Primary to 600A:
Link copied. Please paste this link to share this article on your social media post.
Summation CTs with 5A or 1A outputs work with any power meter supporting those inputs. The meter is blind to what is creating those currents.
Link copied. Please paste this link to share this article on your social media post.
At the customer the IEM3255 with Summation CTs shows only half of the real current.
What could be the reason?
Link copied. Please paste this link to share this article on your social media post.
The connections - particularly of the primaries into the summation CT may be suspect and you need to think about the proportions and size of the summing.
As I mentioned before, if it's a true 5A or 1A output, the summation of the induced current must always be less than this. Please provide the make/model - datasheet on the summation CT you are using.
Link copied. Please paste this link to share this article on your social media post.
this is only half of current, and only half power.
its a KUW1/30-200 CT from Janitza
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
This is actually Cable split core current transformer - they should probably have something like this, too:
Best regards,
Bojan
Link copied. Please paste this link to share this article on your social media post.
Hi Bojan,
yes they have a 1+1 but i think the summation does not work.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Exactly - Bojan's example is exactly right. It adds up the primaries, the proportions of which need to be added together.
That said - are you using a mix of 1A and 5A CTs going into the Summation CT?
Link copied. Please paste this link to share this article on your social media post.
Hi Bojan,
you are absolutely right. For 1+1 it sould be set to 400A. For 1+1+1 is should be set to 600A
Thank you very much
Link copied. Please paste this link to share this article on your social media post.
Hi,
no it is only 1+1 or 1+1+1