IEEEFloat format modbus slave
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
You are correct that the ION7650 meter does not support IEEE float formats in the modbus slave modules. Below is a copy from the ION Reference document "NOTE: The registers and settings available in this module depend on the device or node you are configuring, as well as its firmware and template versions. Not all registers or settings are available on all devices or the Virtual Processor, and labels may vary."
If you were to look at the modbus slave module of the PM8000/ION7400/ION9000, you would see the option to select IEEE Float. This is why the option is listed in ION Reference.
You are correct that the ION7650 meter does not support IEEE float formats in the modbus slave modules. Below is a copy from the ION Reference document "NOTE: The registers and settings available in this module depend on the device or node you are configuring, as well as its firmware and template versions. Not all registers or settings are available on all devices or the Virtual Processor, and labels may vary."
If you were to look at the modbus slave module of the PM8000/ION7400/ION9000, you would see the option to select IEEE Float. This is why the option is listed in ION Reference.