Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

IEC 61850 in 10 MB ION 7650

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • IEC 61850 in 10 MB ION 7650
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa360183_brid
sesa360183_brid Leader
Leader

Posted: ‎2016-07-18 11:51 AM

0 Likes
2
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-18 11:51 AM

IEC 61850 in 10 MB ION 7650

Hi,

According to the datasheet of ION7650, only 5MB ION7650 meters can contain the IEC61850 protocol. However, according to the "IEC61850 and IONTechnology" document, "for meters with firmware earlier than v400, upgrading a 10 MB meter with IEC 61850 firmware will reduce the logging memory to 5 MB".

Does that mean that if the meter has firmware v400 and above, 10MB ION7650 meters can have the IEC61850 protocol (without reducing logging memory to 5MB)?

Hope someone can clarify. Thank you!

Lorenz

Tags (2)
  • Tags:
  • iec61850
  • ion7650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa360183_brid
sesa360183_brid Leader
Leader

Posted: ‎2016-08-08 07:12 AM

0 Likes
0
1810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-08 07:12 AM

Hi,

I would just like to share the response from Advanced Tech Support:

Please find below release note description of ION7650 V400 and above.

V400 is a general firmware release that adds support for new metering hardware. In addition this firmware release reduces the 7x50e and 7x50s variants into one allowing for IEC61850 and 10Meg of logging memory to occur upon the same device. V400 adds compatibility for the -05 hardware revision option. This can be found as the last two digits of a meters serial number. V400 will NOT be compatible with previous versions of hardware ( -04 or earlier). In addition previous firmware revisions (pre V400) will not be compatible with the -05 hardware. We have consolidated the e (IEC61850) and s (standard) variants into one release. This means ALL devices ordered with V400 will now contain IEC61850 functionality as well as contain the 10M logging memory. Both features can be implemented in frameworks simultaneously. NOTE: To support the new features in v400, download the latest version of ION Setup from the website.

Hope it helps!

ID => FA221448

Title => How to find the Firmware Version or Serial Number of any ION or ACM device using ION Setup

URL => http://www.schneider-electric.com/support/index?page=content&country=APS_GLOBAL&lang=en&locale=en_US...


Best Regards

Abhishek Sharma

See Answer In Context

Reply
Replies 2
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2016-08-03 10:07 AM

0 Likes
0
1811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-03 10:07 AM

The implementation of IEC61850 required us to sacrifice some logging memory on the old ION7650 platform as we didn't have the sufficient flash storage to allow us to implement the feature.  Devices which only previously had 5 MB memory still had 5 MB of unallocated flash still so those models which upgraded could use the unused 5 MB for IEC61850 but those that had all 10 MB allocated for log storage had to be reduced to add IEC61850.

All IEC61850 firmware for ION7650 will only have 5 MB of available logging memory.  Switching to a non-IEC1850 firmware will allow you to have 10 MB of logging memory again if you purchased it with 10 MB in the first place.

Reply
sesa360183_brid
sesa360183_brid Leader
Leader

Posted: ‎2016-08-08 07:12 AM

0 Likes
0
1810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-08-08 07:12 AM

Hi,

I would just like to share the response from Advanced Tech Support:

Please find below release note description of ION7650 V400 and above.

V400 is a general firmware release that adds support for new metering hardware. In addition this firmware release reduces the 7x50e and 7x50s variants into one allowing for IEC61850 and 10Meg of logging memory to occur upon the same device. V400 adds compatibility for the -05 hardware revision option. This can be found as the last two digits of a meters serial number. V400 will NOT be compatible with previous versions of hardware ( -04 or earlier). In addition previous firmware revisions (pre V400) will not be compatible with the -05 hardware. We have consolidated the e (IEC61850) and s (standard) variants into one release. This means ALL devices ordered with V400 will now contain IEC61850 functionality as well as contain the 10M logging memory. Both features can be implemented in frameworks simultaneously. NOTE: To support the new features in v400, download the latest version of ION Setup from the website.

Hope it helps!

ID => FA221448

Title => How to find the Firmware Version or Serial Number of any ION or ACM device using ION Setup

URL => http://www.schneider-electric.com/support/index?page=content&country=APS_GLOBAL&lang=en&locale=en_US...


Best Regards

Abhishek Sharma

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore