Dear All,
I have question regarding to iEM3210.
How log the maximum distance of cable if we use hardwire cable connected from intelligent manager to iEM3210?
If the needed is within 200 m, is it the pulse output still detected?
Thank you in advance.
Parlindungan Sitorus
Link copied. Please paste this link to share this article on your social media post.
Hello,
I would say that 200-300 meters will not be a problem - perhaps even higher.
It all depends on the cable used and you need to maintain the voltage between 5 – 30 V DC (as stated in the user guide/installation guide).
Use twisted shielded cable on long distances (0.75mm^2 / 1mm^2) and calculate the voltage drop: Voltage Drop Calculator