Hi all,
When I select 256x7 waveform format in the PM8000 (whether through ION Setup or Designer), I don't get the waveform tick boxes to graph in PME after a manual trigger. I have no problem capturing 128x14 or any of the other format waveforms in the PM8000. In the screen shot below/attached, I have currents set at 128 and Voltages set to 256 to demonstrate. The voltages do not have the tick boxes and the currents do. (If all V & I are set to 128 then I get all V & I tick boxes, if all are set to 256 I get no tick boxes). My other settings seem OK (Depth: 30, Circular, Delay/Post: 3 (and tried 0)).
Dan
Link copied. Please paste this link to share this article on your social media post.
Global Support gave us the solution.
Its just a matter of changing the default SQL query associated with the sag/swell button on the PM8000 Power Quality Page.
1. Right click sag/swell button in Vista, go to "Query" tab, "Edit SQL",
2. Modify the query to return data of higher sampling frequency: i.e. change "WHERE SamplingFrequency < 8000" to "WHERE SamplingFrequency < 15000 to view 256 samples/cycle waveforms (i.e. 12,800 samples per second for 50Hz). Note that it needs changing in multiple places...
Link copied. Please paste this link to share this article on your social media post.
Hi all,
I just thought I'd update you on this. Power Solutions Global Tech Support have replicated this issue in PME 8.1 and 8.2. It appears to be an "out-of-the-box" issue with PME. The waveforms are being captured but not collected by PME for this particular device and waveform format. It has been passed to software R&D.... I'll keep this updated....
Link copied. Please paste this link to share this article on your social media post.
Global Support gave us the solution.
Its just a matter of changing the default SQL query associated with the sag/swell button on the PM8000 Power Quality Page.
1. Right click sag/swell button in Vista, go to "Query" tab, "Edit SQL",
2. Modify the query to return data of higher sampling frequency: i.e. change "WHERE SamplingFrequency < 8000" to "WHERE SamplingFrequency < 15000 to view 256 samples/cycle waveforms (i.e. 12,800 samples per second for 50Hz). Note that it needs changing in multiple places...