Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Having trouble capturing a 256 samples/cycle waveform with the PM8000...

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Having trouble capturing a 256 samples/cycle waveform with the PM8000...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
daniel_parker_p
daniel_parker_p
Mentor

Posted: ‎2017-05-18 08:52 PM

0 Likes
2
2374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-18 08:52 PM

Having trouble capturing a 256 samples/cycle waveform with the PM8000...

Hi all,

When I select 256x7 waveform format in the PM8000 (whether through ION Setup or Designer), I don't get the waveform tick boxes to graph in PME after a manual trigger. I have no problem capturing 128x14 or any of the other format waveforms in the PM8000. In the screen shot below/attached, I have currents set at 128 and Voltages set to 256 to demonstrate.  The voltages do not have the tick boxes and the currents do.  (If all V & I are set to 128 then I get all V & I tick boxes, if all are set to 256 I get no tick boxes). My other settings seem OK (Depth: 30, Circular, Delay/Post: 3 (and tried 0)).

Dan

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
daniel_parker_p
daniel_parker_p
Mentor

Posted: ‎2017-06-20 12:20 AM

1 Like
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-20 12:20 AM

Global Support gave us the solution.

Its just a matter of changing the default SQL query associated with the sag/swell button on the PM8000 Power Quality Page.

1. Right click sag/swell button in Vista, go to "Query" tab, "Edit SQL",

2. Modify the query to return data of higher sampling frequency: i.e. change "WHERE SamplingFrequency < 8000" to "WHERE SamplingFrequency < 15000 to view 256 samples/cycle waveforms (i.e. 12,800 samples per second for 50Hz). Note that it needs changing in multiple places...

See Answer In Context

Reply
Replies 2
daniel_parker_p
daniel_parker_p
Mentor

Posted: ‎2017-05-30 10:41 PM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-30 10:41 PM

Hi all,

I just thought I'd update you on this. Power Solutions Global Tech Support have replicated this issue in PME 8.1 and 8.2. It appears to be an "out-of-the-box" issue with PME. The waveforms are being captured but not collected by PME for this particular device and waveform format. It has been passed to software R&D.... I'll keep this updated....

Reply
daniel_parker_p
daniel_parker_p
Mentor

Posted: ‎2017-06-20 12:20 AM

1 Like
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-20 12:20 AM

Global Support gave us the solution.

Its just a matter of changing the default SQL query associated with the sag/swell button on the PM8000 Power Quality Page.

1. Right click sag/swell button in Vista, go to "Query" tab, "Edit SQL",

2. Modify the query to return data of higher sampling frequency: i.e. change "WHERE SamplingFrequency < 8000" to "WHERE SamplingFrequency < 15000 to view 256 samples/cycle waveforms (i.e. 12,800 samples per second for 50Hz). Note that it needs changing in multiple places...

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore