New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
FAQInjection SignalWhere can I find the value of injection signals for each IMD?
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2015-06-2207:51 AM
For XM300C/XML3xx, there are 2 modes, normal mode with low voltage/current and boost mode with high voltage/current. The IMD changes the mode when Ri cross the alarm threshold. Below is the injection value:
Link copied. Please paste this link to share this article on your social media post.
2015-10-2205:01 AM
For IM400, there are 3 normal mode and 1 boost mode with locating application and when default exist, see diagram below:
in boost mode the IM400 voltage generator is a little more higher(150Vp) and the signal is square 2.5Hz, Below is a shape of the Vf voltage on Rf when IM400 connected with it:
Vfpp=3V Vfp=1.5V
conditions:
IM400 fault threshold = 0.5Kohms, IM400 in locating mode
Rf=400 ohms => IM400 in boost mode with 150Vp scare signal generated
If calculation :
If= Vfp/Rf = 1.5/400 = 0.00375A
this current is closed to the maximum If current (Rf=0) generated by IM400