Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
We have been using in the past the BITRONIC M871 for electrical disturbance recording for at least the three currents and three voltage plus some digital signals as tripping signals, breaker position...
The question is if the ION 7650 colud record in the COMTRADE format this signals for post-mortem analisys and if they can be for example as 2 or 3 second recording and can start recording with a digital signal with pre or post trigger.
Link copied. Please paste this link to share this article on your social media post.
Yes, the ION7650 can be configured to record waveforms in rapid succession in comtrade format that are trigged by it's digital inputs.
Unfortunately it was found that, in this configuration, the comtrade records are sometimes missing/corrupted. A firmware release to fix this issue is scheduled for later this year.