Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84245members
353345posts

Electrical Disturbance recoder ION 7650

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa165289
Cadet
Cadet
0 Likes
1
204

Electrical Disturbance recoder ION 7650

We have been using in the past the BITRONIC M871 for electrical disturbance recording for at least the three currents and three voltage plus some digital signals as tripping signals, breaker position...

The question is if the ION 7650 colud record in the COMTRADE format this signals for post-mortem analisys and if they can be for example as 2 or 3 second recording and can start recording with a digital signal with pre or post trigger.

1 Reply 1
DanL
Commander Commander
Commander
0 Likes
0
157

Re: Electrical Disturbance recoder ION 7650

Yes, the ION7650 can be configured to record waveforms in rapid succession in comtrade format that are trigged by it's digital inputs.

Unfortunately it was found that, in this configuration, the comtrade records are sometimes missing/corrupted. A firmware release to fix this issue is scheduled for later this year.