As per the latest catalog, there is a note for 0.2s class accuracy support for 3PH,4W configuration.
Wanted to check if the same ordering code of 0.2 can be used for the same.
Link copied. Please paste this link to share this article on your social media post.
Hi@Hitesh14 Yes, you are correct. That note is not accurate. For active energy, it's Class 0.2 as per IEC 62053-22 for a 3P4W system. The catalog is old one and needs to be corrected. Please refer to the latest user manual specification.
BR,
Akash
Link copied. Please paste this link to share this article on your social media post.
Hello @Jesus_Diaz ,
Do you know who would be able to answer the question about EM6400 meter?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Hitesh14,
Do you mean which commercial reference supports 0.2 for 3PH, 4W configuration?
According to the catalog, the commercial reference METSEEM6400NGRSCL2 will provide Class 0.2S active energy accuracy per IEC 62053-22 standard in 3PH, 4W configuration.
Best regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi,
as per the LOB responsible the note given in the catalog is a error.
Link copied. Please paste this link to share this article on your social media post.
Hi@Hitesh14 Yes, you are correct. That note is not accurate. For active energy, it's Class 0.2 as per IEC 62053-22 for a 3P4W system. The catalog is old one and needs to be corrected. Please refer to the latest user manual specification.
BR,
Akash