Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

EM4800 kWh intervals

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • EM4800 kWh intervals
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
MatthewP
MatthewP Troubleshooter
Troubleshooter

Posted: ‎2014-07-16 01:41 PM

0 Likes
3
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-16 01:41 PM

EM4800 kWh intervals

Wondering if I could get a detailed explanation into the following.

Using the EM4800 configuration tool I configure 15 minutes recording intervals (under intervals tab) to log Wh, VARh, VAh, demand.

To reduce the frequency of the "uploading data..." message that appears on the device display when the meter attempts to FTP is logs (This is rather annoying for field techs trying to see readings from the front panel) I set the "Reporting schdule" period to 60 minutes.

Energy interval data is logged every 15 minutes however cummulative energy is only logged every hour in this case. Setting the "Reporting schedule" to 15 minutes results in the cummulative energy values being logged now every 15minutes.

So the "Reporting Schedule" appears to be directly tied to the interval that cummulative energy values are logged at instead of the recording interval. Why???

This is on EM4800 running v1.46 firmware.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
greg_expoenergy
greg_expoenergy
Mentor

Posted: ‎2018-06-23 01:00 AM

0 Likes
2
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-23 01:00 AM

As I understand matters your reporting interval should be set at the max log interval.

If you set at 1 hour then you expect 4 values for 15 min interval and 1 value for 1 hr interval.

However, if you set the report interval less the the maximum log interval it causes the 1hr log to be reported at 15 min intervals.

Interval values apply an integrator reset at the end of each interval whereas accumulative integrator values never reset (except at max rollover) so in the end it does not matter.

In other ION meters which may have several logs I have found that if you set one log to log at say 30 min and the other to log at 5 min then when you look at the 30 min log from and each contains the same log variable then the PME database it will contain the 5 min values. This is a known issue within PME as it only stores the same data value for each variable once even though there are two physically separate logs on the meter? Weird but true

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2018-06-24 06:41 PM

0 Likes
1
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-24 06:41 PM

Values are not saved in the database based on the recorder it came from but against the source and measurement.  This means any data logged from a particular register on the device, even if it comes from different recorders, will be saved against the same source and measurement.  One side effect of this is if two recorders with the same input register but with different periods then the data will appear to be the superset of all the recorders.

Reply
greg_expoenergy
greg_expoenergy
Mentor

Posted: ‎2018-06-24 07:42 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-24 07:42 PM

Correct and which is a pain in the butt. The only way to get rid of this is to do SQL filtering via the Vista Query Wizard but which does not work as I have shown and raised elsewhere.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore