EM4800 kWh intervals

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • EM4800 kWh intervals
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
MatthewP
Lt. Commander MatthewP Lt. Commander
Lt. Commander

Posted: ‎2014-07-16 01:41 PM

0 Likes
3
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-16 01:41 PM

EM4800 kWh intervals

Wondering if I could get a detailed explanation into the following.

Using the EM4800 configuration tool I configure 15 minutes recording intervals (under intervals tab) to log Wh, VARh, VAh, demand.

To reduce the frequency of the "uploading data..." message that appears on the device display when the meter attempts to FTP is logs (This is rather annoying for field techs trying to see readings from the front panel) I set the "Reporting schdule" period to 60 minutes.

Energy interval data is logged every 15 minutes however cummulative energy is only logged every hour in this case. Setting the "Reporting schedule" to 15 minutes results in the cummulative energy values being logged now every 15minutes.

So the "Reporting Schedule" appears to be directly tied to the interval that cummulative energy values are logged at instead of the recording interval. Why???

This is on EM4800 running v1.46 firmware.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
greg_expoenergy
Lt. Commander greg_expoenergy
Lt. Commander

Posted: ‎2018-06-23 01:00 AM

0 Likes
2
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-23 01:00 AM

As I understand matters your reporting interval should be set at the max log interval.

If you set at 1 hour then you expect 4 values for 15 min interval and 1 value for 1 hr interval.

However, if you set the report interval less the the maximum log interval it causes the 1hr log to be reported at 15 min intervals.

Interval values apply an integrator reset at the end of each interval whereas accumulative integrator values never reset (except at max rollover) so in the end it does not matter.

In other ION meters which may have several logs I have found that if you set one log to log at say 30 min and the other to log at 5 min then when you look at the 30 min log from and each contains the same log variable then the PME database it will contain the 5 min values. This is a known issue within PME as it only stores the same data value for each variable once even though there are two physically separate logs on the meter? Weird but true

Reply
Hal_Etheridge
Janeway Hal_Etheridge Janeway
Janeway

Posted: ‎2018-06-24 06:41 PM

0 Likes
1
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-24 06:41 PM

Values are not saved in the database based on the recorder it came from but against the source and measurement.  This means any data logged from a particular register on the device, even if it comes from different recorders, will be saved against the same source and measurement.  One side effect of this is if two recorders with the same input register but with different periods then the data will appear to be the superset of all the recorders.

Reply
greg_expoenergy
Lt. Commander greg_expoenergy
Lt. Commander

Posted: ‎2018-06-24 07:42 PM

0 Likes
0
873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-24 07:42 PM

Correct and which is a pain in the butt. The only way to get rid of this is to do SQL filtering via the Vista Query Wizard but which does not work as I have shown and raised elsewhere.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of