Hi All,
This to bring in your notice that EM4800 1.31 and below versions doesn't support all the function as well as inconsistent in data logging with PME 7.2.1
EM4800 1.46V onwards supports with PME 7.2.1 . I would be interested to know the latest firmware of EM4800 and its features, availability & compatibility ??
Regards
Ganesh
Link copied. Please paste this link to share this article on your social media post.
Can anyone tell me where to find newer firmware for EM4800's
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Hi John,
Please refer the RESL205973 But I am not sure other than 1.46V the latest version are realised,
RESOLUTION: How to upgrade firmware on a PowerLogic EM4800
Regards
Ganesh
Link copied. Please paste this link to share this article on your social media post.
Hi All,
Latest version of EM4800 Configuration Tool will enable all the latest features in EM4800, this works fine with PME latest version – please find it and download using the link below:
https://www.dropbox.com/sh/eykubufyx6cfl43/1ySMvnJKEy/Configuration%20Tool
Link copied. Please paste this link to share this article on your social media post.
All our EM4800s runs on firmware 1.46 without issues with the latest version of PME7.2.2
Backfilling of data etc. works well.
But the only problem we are running into is that it seems that the "Maximum Current per phase" is not being logged onboard. Although, it is being advertised on the latest driver.
Link copied. Please paste this link to share this article on your social media post.
Haven't heard of this issue before.
Can you provide me with the following diagnostic information:
1. Access the EM4800 device using a standard web browser by typing the IP address in the address bar
2. Click on Info
3. Click on Intervals
You will be able to view the onboard data log. Each record will be displayed in the following format: Timestamp, Record type (displayed as a number), Data
For example: 2014/06/06,10:30,40,0.049,0.046,0.052,0.056,0.048,0.037,0.044,0.053 where 40 is the record type.
In the list, do you see records with record type 40,41,42. If the records are visible then it means Maximum Current log is available in the device.
I am assuming that you have selected Peak Current while configuring the device.
Link copied. Please paste this link to share this article on your social media post.
Hi Anirbhan,
I don't see entry 40 in the logs.
To be honest, I also didn't notice the option to select peak current when
configuring the meter - please see attached screen shot? Maybe I am
missing something?
Latest Intervals:
2014/06/09,12:30,2,1157035,7131217,4465306,6340173,14989569,18660903,11962716,6353429,12890327,4543339,7028321,2591019,6941695,9724375,70291,7901363,5630841,1511575,1109319,3527724,66241,124594,96220,447237
2014/06/09,12:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,12:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,12:30,1,3,216,133,194,414,612,370,199,311,139,241,194,177,338,0,243,208,57,69,110,8,17,3,14
2014/06/09,12:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,12:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,12:15,2,1157032,7131001,4465173,6339979,14989155,18660291,11962346,6353230,12890016,4543200,7028080,2590825,6941518,9724037,70291,7901120,5630633,1511518,1109250,3527614,66233,124577,96217,447223
2014/06/09,12:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,12:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,12:15,1,3,223,137,199,427,633,380,207,320,144,249,199,183,348,0,249,218,59,71,113,9,18,4,14
2014/06/09,12:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,12:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,12:00,2,1157029,7130778,4465036,6339780,14988728,18659658,11961966,6353023,12889696,4543056,7027831,2590626,6941335,9723689,70291,7900871,5630415,1511459,1109179,3527501,66224,124559,96213,447209
2014/06/09,12:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,12:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,12:00,1,3,223,138,202,428,623,380,206,319,144,251,200,183,345,0,249,215,59,71,113,8,17,3,14
2014/06/09,12:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,12:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:45,2,1157026,7130555,4464898,6339578,14988300,18659035,11961586,6352817,12889377,4542912,7027580,2590426,6941152,9723344,70291,7900622,5630200,1511400,1109108,3527388,66216,124542,96210,447195
2014/06/09,11:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,11:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,11:45,1,3,231,142,210,441,645,392,213,331,148,259,205,190,361,0,258,226,60,73,117,8,18,3,15
2014/06/09,11:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:30,2,1157023,7130324,4464756,6339368,14987859,18658390,11961194,6352604,12889046,4542764,7027321,2590221,6940962,9722983,70291,7900364,5629974,1511340,1109035,3527271,66208,124524,96207,447180
2014/06/09,11:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,11:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,11:30,1,3,218,132,197,414,609,369,199,311,139,243,193,177,341,0,242,218,57,68,110,8,18,3,13
2014/06/09,11:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:15,2,1157020,7130106,4464624,6339171,14987445,18657781,11960825,6352405,12888735,4542625,7027078,2590028,6940785,9722642,70291,7900122,5629756,1511283,1108967,3527161,66200,124506,96204,447167
2014/06/09,11:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,11:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,11:15,1,3,224,138,201,428,639,380,207,321,144,248,200,183,347,0,250,226,59,71,113,9,17,3,14
2014/06/09,11:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:00,2,1157017,7129882,4464486,6338970,14987017,18657142,11960445,6352198,12888414,4542481,7026830,2589828,6940602,9722295,70291,7899872,5629530,1511224,1108896,3527048,66191,124489,96201,447153
2014/06/09,11:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,11:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,11:00,1,3,225,137,201,427,631,381,206,323,144,249,199,184,350,0,250,226,59,71,113,8,18,4,15
2014/06/09,11:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,11:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:45,2,1157014,7129657,4464349,6338769,14986590,18656511,11960064,6351992,12888091,4542337,7026581,2589629,6940418,9721945,70291,7899622,5629304,1511165,1108825,3526935,66183,124471,96197,447138
2014/06/09,10:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,10:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,10:45,1,3,232,142,208,442,668,391,213,333,149,257,206,189,359,0,258,234,61,73,117,8,18,3,14
2014/06/09,10:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:30,2,1157011,7129425,4464207,6338561,14986148,18655843,11959673,6351779,12887758,4542188,7026324,2589423,6940229,9721586,70291,7899364,5629070,1511104,1108752,3526818,66175,124453,96194,447124
2014/06/09,10:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,10:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,10:30,1,3,217,133,196,414,621,369,199,313,139,242,194,178,337,0,242,218,58,69,110,8,17,3,14
2014/06/09,10:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:15,2,1157008,7129208,4464074,6338365,14985734,18655222,11959304,6351580,12887445,4542049,7026082,2589229,6940051,9721249,70291,7899122,5628852,1511046,1108683,3526708,66167,124436,96191,447110
2014/06/09,10:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,10:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,10:15,1,3,224,138,201,429,638,381,206,319,144,247,200,183,351,0,251,223,60,71,113,9,18,3,14
2014/06/09,10:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:00,2,1157005,7128984,4463936,6338164,14985305,18654584,11958923,6351374,12887126,4541905,7025835,2589029,6939868,9720898,70291,7898871,5628629,1510986,1108612,3526595,66158,124418,96188,447096
2014/06/09,10:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,10:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,10:00,1,3,224,137,200,428,649,380,206,320,144,248,199,183,349,0,250,219,58,70,114,8,18,3,14
2014/06/09,10:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,10:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:45,2,1157002,7128760,4463799,6337964,14984877,18653935,11958543,6351168,12886806,4541761,7025587,2588830,6939685,9720549,70291,7898621,5628410,1510928,1108542,3526481,66150,124400,96185,447082
2014/06/09,09:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,09:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,09:45,1,3,231,142,208,442,672,393,213,329,149,257,206,191,360,0,256,226,60,73,117,8,18,4,15
2014/06/09,09:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:30,2,1156999,7128529,4463657,6337756,14984435,18653263,11958150,6350955,12886477,4541612,7025330,2588624,6939494,9720189,70291,7898365,5628184,1510868,1108469,3526364,66142,124382,96181,447067
2014/06/09,09:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,09:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,09:30,1,3,216,134,193,415,631,367,199,309,139,242,193,178,336,0,243,209,57,69,109,8,17,3,14
2014/06/09,09:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:15,2,1156996,7128313,4463523,6337563,14984020,18652632,11957783,6350756,12886168,4541473,7025088,2588431,6939316,9719853,70291,7898122,5627975,1510811,1108400,3526255,66134,124365,96178,447053
2014/06/09,09:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,09:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,09:15,1,3,224,137,202,428,654,382,206,321,144,250,199,183,350,0,250,216,59,70,113,8,18,3,14
2014/06/09,09:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:00,2,1156993,7128089,4463386,6337361,14983592,18651978,11957401,6350550,12885847,4541329,7024838,2588232,6939133,9719503,70291,7897872,5627759,1510752,1108330,3526142,66126,124347,96175,447039
2014/06/09,09:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,09:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,09:00,1,3,223,138,201,428,655,380,206,320,145,248,200,184,349,0,254,214,59,71,114,9,17,3,14
2014/06/09,09:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,09:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:45,2,1156990,7127866,4463248,6337160,14983164,18651323,11957021,6350344,12885527,4541184,7024590,2588032,6938949,9719154,70291,7897618,5627545,1510693,1108259,3526028,66117,124330,96172,447025
2014/06/09,08:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,08:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,08:45,1,3,231,141,208,442,670,392,212,334,148,256,207,189,359,0,263,225,61,73,117,8,18,4,15
2014/06/09,08:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:30,2,1156987,7127635,4463107,6336952,14982722,18650653,11956629,6350132,12885193,4541036,7024334,2587825,6938760,9718795,70291,7897355,5627320,1510632,1108186,3525911,66109,124312,96168,447010
2014/06/09,08:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,08:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,08:30,1,3,216,134,193,416,639,369,200,317,140,241,193,178,338,0,248,209,57,68,109,8,18,3,13
2014/06/09,08:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:15,2,1156984,7127419,4462973,6336759,14982306,18650014,11956260,6349932,12884876,4540896,7024093,2587632,6938582,9718457,70291,7897107,5627111,1510575,1108118,3525802,66101,124294,96165,446997
2014/06/09,08:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,08:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,08:15,1,3,224,137,200,429,661,381,205,327,145,253,200,183,350,0,254,221,59,71,114,9,17,3,15
2014/06/09,08:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:00,2,1156981,7127195,4462836,6336559,14981877,18649353,11955879,6349727,12884549,4540751,7023840,2587432,6938399,9718107,70291,7896853,5626890,1510516,1108047,3525688,66092,124277,96162,446982
2014/06/09,08:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,08:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,08:00,1,3,223,137,201,428,652,381,203,321,144,251,199,183,349,0,256,219,59,70,113,8,18,3,14
2014/06/09,08:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,08:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:45,2,1156978,7126972,4462699,6336358,14981449,18648701,11955498,6349524,12884228,4540607,7023589,2587233,6938216,9717758,70291,7896597,5626671,1510457,1107977,3525575,66084,124259,96159,446968
2014/06/09,07:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,07:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,07:45,1,3,233,142,206,441,658,392,207,331,149,255,206,189,359,0,264,226,60,73,117,8,18,4,14
2014/06/09,07:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:30,2,1156975,7126739,4462557,6336152,14981008,18648043,11955106,6349317,12883897,4540458,7023334,2587027,6938027,9717399,70291,7896333,5626445,1510397,1107904,3525458,66076,124241,96155,446954
2014/06/09,07:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,07:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,07:30,1,3,218,133,195,415,619,368,195,314,140,241,194,178,339,0,248,211,57,69,110,8,17,3,14
2014/06/09,07:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:15,2,1156972,7126521,4462424,6335957,14980593,18647424,11954738,6349122,12883583,4540318,7023093,2586833,6937849,9717060,70291,7896085,5626234,1510340,1107835,3525348,66068,124224,96152,446940
2014/06/09,07:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,07:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,07:15,1,3,225,138,200,427,635,379,202,322,145,248,199,183,346,0,256,218,59,70,113,9,18,3,14
2014/06/09,07:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:00,2,1156969,7126296,4462286,6335757,14980166,18646789,11954359,6348920,12883261,4540173,7022845,2586634,6937666,9716714,70291,7895829,5626016,1510281,1107765,3525235,66059,124206,96149,446926
2014/06/09,07:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,07:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,07:00,1,3,225,137,201,427,627,381,201,321,144,248,200,183,347,0,253,220,58,71,114,8,18,3,14
2014/06/09,07:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,07:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:45,2,1156966,7126071,4462149,6335556,14979739,18646162,11953978,6348719,12882940,4540029,7022597,2586434,6937483,9716367,70291,7895576,5625796,1510223,1107694,3525121,66051,124188,96146,446912
2014/06/09,06:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,06:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,06:45,1,3,225,138,201,428,634,380,201,321,144,248,199,183,348,0,252,219,59,70,113,8,17,3,15
2014/06/09,06:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:30,2,1156963,7125846,4462011,6335355,14979311,18645528,11953598,6348518,12882619,4539885,7022349,2586235,6937300,9716019,70291,7895324,5625577,1510164,1107624,3525008,66043,124171,96143,446897
2014/06/09,06:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,06:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,06:30,1,3,223,137,200,426,631,379,202,323,144,244,200,184,349,0,255,218,59,71,113,8,18,4,14
2014/06/09,06:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:15,2,1156960,7125623,4461874,6335155,14978885,18644897,11953219,6348316,12882296,4539741,7022105,2586035,6937116,9715670,70291,7895069,5625359,1510105,1107553,3524895,66035,124153,96139,446883
2014/06/09,06:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,06:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,06:15,1,3,224,138,199,427,621,380,201,323,144,241,200,183,348,0,253,221,59,71,113,9,17,3,14
2014/06/09,06:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:00,2,1156957,7125399,4461736,6334956,14978458,18644276,11952839,6348115,12881973,4539597,7021864,2585835,6936933,9715322,70291,7894816,5625138,1510046,1107482,3524782,66026,124136,96136,446869
2014/06/09,06:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,06:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,06:00,1,3,224,137,200,427,613,379,201,323,144,240,199,183,348,0,250,216,59,70,113,8,18,3,14
2014/06/09,06:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,06:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:45,1,3,223,138,200,427,609,381,201,321,144,240,199,183,348,0,249,218,59,70,114,8,18,3,14
2014/06/09,05:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:30,2,1156951,7124952,4461461,6334556,14977604,18643054,11952079,6347713,12881329,4539309,7021384,2585437,6936567,9714626,70291,7894317,5624704,1509928,1107342,3524555,66010,124100,96130,446841
2014/06/09,05:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,05:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,05:30,2,1156951,7124952,4461461,6334556,14977604,18643054,11952079,6347713,12881329,4539309,7021384,2585437,6936567,9714626,70291,7894317,5624704,1509928,1107342,3524555,66010,124100,96130,446841
2014/06/09,05:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,05:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,05:30,1,3,223,137,202,427,598,379,202,323,144,239,200,183,348,0,246,214,58,71,113,9,17,3,14
2014/06/09,05:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:15,2,1156948,7124729,4461324,6334354,14977177,18642456,11951700,6347511,12881006,4539165,7021145,2585237,6936384,9714278,70291,7894071,5624490,1509870,1107271,3524442,66001,124083,96127,446827
2014/06/09,05:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,05:15,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,05:15,1,3,222,137,200,427,600,379,201,323,144,238,199,183,349,0,246,214,59,70,113,8,18,4,15
2014/06/09,05:15,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:15,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:00,2,1156945,7124507,4461187,6334154,14976750,18641856,11951321,6347310,12880683,4539021,7020907,2585038,6936201,9713929,70291,7893825,5624276,1509811,1107201,3524329,65993,124065,96123,446812
2014/06/09,05:00,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,05:00,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,05:00,1,3,223,137,199,425,594,379,201,320,143,239,199,184,348,0,245,215,59,71,113,8,18,3,14
2014/06/09,05:00,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,05:00,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,04:45,2,1156942,7124284,4461050,6333955,14976325,18641262,11950942,6347109,12880363,4538878,7020668,2584839,6936017,9713581,70291,7893580,5624061,1509752,1107130,3524216,65985,124047,96120,446798
2014/06/09,04:45,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,04:45,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,04:45,1,3,223,138,199,425,589,380,201,320,144,237,199,183,348,0,245,217,59,70,114,8,17,3,14
2014/06/09,04:45,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,04:45,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,04:30,2,1156939,7124061,4460912,6333756,14975900,18640673,11950562,6346908,12880043,4538734,7020431,2584640,6935834,9713233,70291,7893335,5623844,1509693,1107060,3524102,65977,124030,96117,446784
2014/06/09,04:30,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
2014/06/09,04:30,33,0,3,2,0,0,0,1,35,0,0,0,0,0,0,125,0,0,0,0,0,0,0,7,87
2014/06/09,04:30,1,3,222,137,199,427,591,379,201,321,144,237,200,183,348,0,247,215,59,70,113,9,18,3,14
2014/06/09,04:30,29,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,04:30,28,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0
2014/06/09,04:15,2,1156936,7123839,4460775,6333557,14975473,18640082,11950183,6346707,12879722,4538590,7020194,2584440,6935651,9712885,70291,7893088,5623629,1509634,1106990,3523989,65968,124012,96114,446770
2014/06/09,04:15,34,19,33,22,0,0,0,0,2,0,0,0,0,0,0,0,0,0,0,0,0,0,11044,0,0
Link copied. Please paste this link to share this article on your social media post.
Hi Arjan,
Does your EM4800 configuration set up look like this , if it doesn't look like this then download the latest version of EM4800 Configuration Tool and re-upload 1.46 v (RESOLUTION: How to upgrade firmware on a PowerLogic EM4800) which will enable all the latest features in EM4800, this works fine with PME latest version https://www.dropbox.com/sh/eykubufyx6cfl43/1ySMvnJKEy/Configuration%20Tool
.
Link copied. Please paste this link to share this article on your social media post.
Thanks ganesh,
Sent from my iPad
Link copied. Please paste this link to share this article on your social media post.
Hi Ganesh,
Do you know if it is possible to upgrade firmware over IP network?
I see that the firmware uploader cannot 'see' devices which are not
directly connected via Level 2 Ethernet.
Is there a way to upload the firmware directly via TFTP via IP network
(Level 3)?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Arjan
It’s not recommended to do software update over the IP network. Request you to connect to device directly
Link copied. Please paste this link to share this article on your social media post.
I upgraded successfully 3 x EM4850 from 1.31 to the latest 4.6 version in ION Enterprise 6.0 Service 1 today, and Demand logs start coming in, but Customer noticed that Real Power Total column is missing in the report.
Is there a workaround for this issue?
Link copied. Please paste this link to share this article on your social media post.
Hi Bojan,
Link copied. Please paste this link to share this article on your social media post.
Hi Bojan,
The Quanitity "present demand" works for us in PME 7.2.2
Please see below screenshot ("Present Demand" = Real Power)
Posted: 2014-12-18 02:07 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Ganesh,
Would you mind re-uploading the latest tool? It looks like it's been deleted. Thanks.