New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
EM4200 and iem3000 On a Daisy-Chain with Link 150
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2017-07-1406:43 AM
EM4200 and iem3000 On a Daisy-Chain with Link 150
TEAM:
We have one EM4200 and twelve iem3000 On a Daisy-Chain with a Link 150. The serial port was set to 9600, None, Stop Bit Automatic. The iem3000 units came in fine but the EM4200 (new Enercept) would not communicate.
The fix is to change the stop bit from Automatic to 1. The iem meters were happy and the EM4200 started working. Even with the stop bit at Automatic Vista did not complain but it also did not return any live data.
NOTE: The latest rev I could find for ION Setup has an EM4200 device type but does not have live data tables for this meter. Had to create a unit in PME for testing.
Regarding the serial port setting Stop bit set to "Automatic" (not "1"): We also experienced this behavior with the Com'X 510. We daisy-chained an EM4900 and an EM4200 to the ComX, and we were able to talk to both meters through the Com'X 510 webpage. However, ION Setup could not communicate with the EM4200 (even though the EM4900 worked fine through ION Setup). We disconnected the EM4200 and hooked it up to the EGX300 instead. ION setup was then able to connect to the EM4200 through the EGX. Not sure if it's the ComX or the EM4200 that's causing this.