EM4200 and iem3000 On a Daisy-Chain with Link 150

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • EM4200 and iem3000 On a Daisy-Chain with Link 150
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
496
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
96
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2017-07-14 06:43 AM

0 Likes
2
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-14 06:43 AM

EM4200 and iem3000 On a Daisy-Chain with Link 150

TEAM:

We have one EM4200 and twelve iem3000 On a Daisy-Chain with a Link 150.  The serial port was set to 9600, None, Stop Bit Automatic.  The iem3000 units came in fine but the EM4200 (new Enercept) would not communicate.

The fix is to change the stop bit from Automatic to 1.  The iem meters were happy and the EM4200 started working.  Even with the stop bit at Automatic Vista did not complain but it also did not return any live data.

NOTE:  The latest rev I could find for ION Setup has an EM4200 device type but does not have live data tables for this meter.  Had to create a unit in PME for testing.

Sincerely,

Michael Franz

Faith Technologies

Tags (6)
  • Tags:
  • daisy-chain
  • em4200
  • iem3000
  • ion setup
  • link 150
  • repair communications
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Anonymous user
Not applicable

Posted: ‎2017-07-18 08:27 AM

1 Like
1
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-18 08:27 AM

Hi Robert Lee​,

Regarding the serial port setting Stop bit set to "Automatic" (not "1"):
We also experienced this behavior with the Com'X 510. We daisy-chained an EM4900 and an EM4200 to the ComX, and we were able to talk to both meters through the Com'X 510 webpage.  However, ION Setup could not communicate with the EM4200 (even though the EM4900 worked fine through ION Setup). 
We disconnected the EM4200 and hooked it up to the EGX300 instead.  ION setup was then able to connect to the EM4200 through the EGX.
Not sure if it's the ComX or the EM4200 that's causing this.

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2017-07-18 08:44 AM

0 Likes
0
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-18 08:44 AM

TEAM:

What make the new Enercept odd is that it has one communication setting, the address.

It is designed to learn the rest by listening to the daisy-chain.  With the Link 150 set to

Automatic on the stop bit the meter appeared incapable of finding its place.

Once we set the Stop Bit to 1 both the Enercept and iem3xxx meters were able to work.

Michael Franz

Faith Technologies

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of