Accusine PCS+ Settings to achieve both Harmonic Filtering and Power Factor Correction
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2019-05-2010:28 PM
Accusine PCS+ Settings to achieve both Harmonic Filtering and Power Factor Correction
Dear Team,
We have a case wherein we need to allocate for both Harmonic Filtering and PF Correction. We intend to set the priority as 100% to Active Harmonic Filtering and 0% to PFC Correction. As per the tabulation and explanation provided in the manual, we are understanding that
"With Harmonic priority set to 100% the unit will output all current necessary to correct the harmonic content. Any output capacity left over will be used to correct PF and/or load balancing:
In our project the requirement is of1004Aas per the simulation study. We need to provide 300A: 3 Nos, 200A: 1 No.totalling to 1100A.
So based on 100% Filtering priority, once the requirement of 1004A is reached, will the unit deliver for Power Factor Correction the balance current available.
Alternatively whats the operation philiosohpy if we use the 90% Filtering and 44% Correction settings