Good day
We have a case with Accusine PCS+ 300A when connected temporarily with a 200A MCCB for power up test, we had issued on earth leakage trip relay upstream whenever the 200A breaker is turned ON. We had 2 units at site with same behaviour. The ELR setting was at 300mA. We tried with 500mA and it was the same. Could it be faulty components?
Has anyone experience this?
TQ
EY
Link copied. Please paste this link to share this article on your social media post.
Hi EY
I think already Mike fry -L4 Expert(Accusine) has replied you on this topic,
Here is the reply from Mike----With ELR you should open the IT switches. See if that corrects the issue.
Posted: 2019-08-05 07:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-06 12:20 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
if you still have not solved the problem, suggest you to contact local support team TSC,
they will create a case in BFO tool and escalate it if will needed .
BR
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-20 07:58 AM
Link copied. Please paste this link to share this article on your social media post.
Hi @sesa108084_brid,
If @Arunprasad helped you to solve your problem, please click on “Accept as Solution” so other members can find the same solution through the search bar. Thank you!
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.