Hello Experts!
Is there any document that states maximum length of power cables for AccuSine?
The longer the cable, the higher it's impedance which (I'm guessing) can become a problem at certain point.
Any ideas?
Best regards,
Sz.
Link copied. Please paste this link to share this article on your social media post.
Hi,
There is no table that states the maximum cable lenght of power cables for AccuSine. Basically the local electrical code must be respected and you also have to make sure that you have enough cables to limit the voltage drop across the cable run, values of 3% to 5% voltage drop are normally used. The AccuSine itself has a +10%/-15% voltage input tolerence.
Link copied. Please paste this link to share this article on your social media post.
Hi,
There is no table that states the maximum cable lenght of power cables for AccuSine. Basically the local electrical code must be respected and you also have to make sure that you have enough cables to limit the voltage drop across the cable run, values of 3% to 5% voltage drop are normally used. The AccuSine itself has a +10%/-15% voltage input tolerence.