M172 Modbus Master - how to reset status 2 indication

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 Modbus Master - how to reset status 2 indication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
76
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
51
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
kor
Ensign kor
Ensign

Posted: ‎2022-11-18 01:24 AM

0 Likes
4
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 01:24 AM

M172 Modbus Master - how to reset status 2 indication

I've problem with installations with TM172 (fw 596.12) as a master  for modbus rtu heat meters network. Sites've worked correctly from few to several dosen minutes  and after that controller indicate .miss on all slave devices with 2 status code, missCnt is increasing. Slave network is terminated correctly and have aplied bias resistors.

To restore communication I've to perform reboot on TM, aftertheat communication returns but again only for certain period and all trouble return.

There is a way to restart RS485-2  port or hold and release all readouts from code without need to reboot controller?

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2022-11-18 02:45 AM

0 Likes
3
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 02:45 AM

Hello,

 

there is not a way to restart the serial (controller can be rebooted using sysWD_Background(0)).

Have you tried to monitor the line with an oscilloscope?

If you disconnect/reconnect slaves or master Modbus connector, does something happen?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
kor
Ensign kor
Ensign

Posted: ‎2022-11-18 05:10 AM

In response to FedericoM
0 Likes
2
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 05:10 AM

Thank you, there are all remote sites but I wiil try to find someone enought brave locally to touch automation box and switch on /off cables. Oscilloscope is out of option at this moment, and from this my previous question about possibility to restart only serial interface without whole controller (from obious reason). If it is not possible I will have to find other workaround solution 

 

    

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-11-18 05:20 AM

In response to kor
0 Likes
1
1251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 05:20 AM

If you use the target blocks sysMbMERTU_FC** you could generat an commication which could be startet and stopped via application. But this way is normally not so fast and not so comfortabel. 

I could be a workaround but not a solving of the real probelm.

The heat meters the only modbus devices you read?

How many heat meter did you read?

Which hardware did you use exactly.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
kor
Ensign kor
Ensign

Posted: ‎2022-11-18 09:40 AM

In response to Bastian_Schmitz
0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 09:40 AM

Temporaily I've supressed this by use of the one of free DO in TM to make a short for about four cycles with 100ms timing task RS485-2 '+' signal to Gnd on port RS485-2 socket. I'm affraid that there could be a problem related to some kind of slave tranceivers because it appears on Modbus RTU for Kamstrup heat meters 601 and I've similar problem witcg Schneider FM40 Uniflair chiller 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of