Posted: 2022-11-15 03:32 AM
I need help regarding how to use TM172 fast digital inputs. As far as I know, digital inputs DI1 and DI2 in the whole line can either be used as regular digital inputs or as fast inputs.
I am sure this is documented somewhere, if so please let me know where to find the documentation. I have checked all the documents I have and could not find it.
Following the convention followed on the published TDVAs I am naming inputs as per the following pic.
I then later reassign them to logical variables within a program called Physical_to_logical_inputs, the same concept used in TDVAs.
So, let´s say I add these new variables like in the picture and add these lines to Physical_to_logical_inputs program:
Status_udiCount1 := FI_Counter1;
Status_udiFreq1 := FI_Frequency1;
Is that all that it takes? In case I only need one fast input, for example DI1, is DI2 still available as a regular input?
What is the unit of FDI Frequency ?
What do FDI*_value and FDI*_reset_counter mean and how are they used ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-15 03:41 AM
Hi,
here below the answers to your questions:
Is that all that it takes?
Yes, it is
In case I only need one fast input, for example DI1, is DI2 still available as a regular input?
Considering che common input, DI2 can be used as regular input
What is the unit of FDI Frequency ?
[Hz/10]
What do FDI*_value and FDI*_reset_counter mean and how are they used ?
FDI*_value is the current status of the input (like when you use it as regular input)
FDI*_reset_counter if set to true allows to reset the number of counted pulses
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-15 03:41 AM
Hi,
here below the answers to your questions:
Is that all that it takes?
Yes, it is
In case I only need one fast input, for example DI1, is DI2 still available as a regular input?
Considering che common input, DI2 can be used as regular input
What is the unit of FDI Frequency ?
[Hz/10]
What do FDI*_value and FDI*_reset_counter mean and how are they used ?
FDI*_value is the current status of the input (like when you use it as regular input)
FDI*_reset_counter if set to true allows to reset the number of counted pulses
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-15 06:04 AM . Last Modified: 2022-11-15 06:28 AM
😀
Pretty simple actually. Thanks.
In the previous post you said :"The frequency is the one of the last period, so you might need to post filter it." Could you explain a little further ?
I noticed there´s a small lag between the time the signal in my scope goes to gnd and the time frequency reads 0 in the PLC. For this application it has no importance but I think that it eventually become important for other uses. Is that what you mean by post-filtering the signal? What kind of filters may be used ?
As a side note: is a pull up resistor advised ?