Posted: 2022-11-19 03:23 AM
There´s a pulse generator available in the basic library. Here´s how to find it and use it.
Hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-19 03:23 AM
There´s a pulse generator available in the basic library. Here´s how to find it and use it.
Hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-20 10:14 PM
And as additional information for a better understanding.
TP creat "only" 1 Puls for the time PT after EN get a TRUE.
Pulse create 1 Puls related to the value of periode and the number of tasks.
If you call Pulse in a timed task with a task time of 100ms the block will creat with a period input of 10 every 1s a true output.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.