Machine Automation Forum
A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-14 07:58 PM
Hi all,
I'm using the M172PDG18R.
If I using a Modbus RTU client, I can see from the M172 side that the client is correctly communicating by using the 'sysMODBUS_msg_received_RS485_1' parameter.
Is there a similar feature, or another method I can use for observing the Modbus TCP interface when the M172 is a server?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-15 05:45 AM
HI,
I don't think we have this same Modbus status variable in TCP.
However, as a:
- Client you can use the System Varaible "sysMbMTcpNodeStatus" to have information on the Modbus TCP communictaion Status.
- Server you have the Variables "sysMbSTcp_SocketServerInfo"
BR
;
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-15 05:45 AM
HI,
I don't think we have this same Modbus status variable in TCP.
However, as a:
- Client you can use the System Varaible "sysMbMTcpNodeStatus" to have information on the Modbus TCP communictaion Status.
- Server you have the Variables "sysMbSTcp_SocketServerInfo"
BR
;