TM171 HMI/Display units

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM171 HMI/Display units
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
66
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Solved
otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-08-08 07:13 AM . Last Modified: ‎2022-08-08 07:14 AM

0 Likes
4
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 07:13 AM . Last Modified: ‎2022-08-08 07:14 AM

TM171 HMI/Display units

I found looking at the TDA_Chiller_Simple project that it is possible to show UDINT units with the TM171 display by using a format named "h" which I assume is configurable somehow. I could not find the information on how to create a new display unit, besides the standard units which appear in the drop-down menu.

 

units.jpg 

Could anyone point me to the right resource ? 

Labels
  • Labels:
  • HVAC
  • Tags:
  • ecostruxure
  • english
  • hvac
  • TM171
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-08-08 11:12 PM

In response to otrotabi
0 Likes
1
1222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 11:12 PM

I mean with "free text" that you can use any unite you like. As example s,min,h,kW,l/min,starts.... but if you use a unite which is not integrated in the drop down menü these value will not influence the LEDs.

But you could see these Unit in Commisioning, Installer and on the webserver.

unite.PNG

If you want to show a value which could be bigger then 9999 in the display I see two ways.

1. You could scale the value via division through 10 or 100. In your program you look on the value, and if the value is bigger then 9999 you divide him through 10. In a second value could you show that these division is active.

It would like the power consumption in a ATV320. If the ATV is new the scale is Wh, after some time it changed to kWh and if the drive is old you see GWh. Through an additional value you could read back the unit.

2. You split the value in two values. The first value shows the first 4 numbers up to 9999 and the second value shows the additional numbers.

 

I would prefer version two. If you want show the start number of a valve or a motor I mostly prefer version 1. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-08-08 07:17 AM

0 Likes
3
1247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 07:17 AM

You could use in general free text in this field. 

But the free text work only in Commisioning and Installer, and in the Webserver if used (TM171P/TM172).
The values which are in the drop down menue are directly alinged to the LEDs.

If you use free text that would not influence the LEDs.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-08-08 08:03 AM

In response to Bastian_Schmitz
0 Likes
2
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 08:03 AM

I actually do not understand wht you mean by "free text" speaking of the TM171. I am familiarized with the TM172 display and how to size the units but not quite so with the TM171.

 

If I simply write "s"  the "Outr" error dissapears showing 0 instead but it is actually not the real value so some configuration is needed.

 

I am trying to find out what is the way to display compressor working hours on the display, which is UDINT type.

 

Again, the Simple Chiller TDVA project has this "s" in the unit, and the working hours show fine on the display but the caveat is that it will only display numbers less than 10000 (<= 9999) which is the maximun size this display will show. I get this "Outr" error  on the screen for bigger numbers (at least in simulation).

 

 

outrange.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-08-08 11:12 PM

In response to otrotabi
0 Likes
1
1223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-08 11:12 PM

I mean with "free text" that you can use any unite you like. As example s,min,h,kW,l/min,starts.... but if you use a unite which is not integrated in the drop down menü these value will not influence the LEDs.

But you could see these Unit in Commisioning, Installer and on the webserver.

unite.PNG

If you want to show a value which could be bigger then 9999 in the display I see two ways.

1. You could scale the value via division through 10 or 100. In your program you look on the value, and if the value is bigger then 9999 you divide him through 10. In a second value could you show that these division is active.

It would like the power consumption in a ATV320. If the ATV is new the scale is Wh, after some time it changed to kWh and if the drive is old you see GWh. Through an additional value you could read back the unit.

2. You split the value in two values. The first value shows the first 4 numbers up to 9999 and the second value shows the additional numbers.

 

I would prefer version two. If you want show the start number of a valve or a motor I mostly prefer version 1. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-08-10 07:28 AM

In response to Bastian_Schmitz
0 Likes
0
1204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-10 07:28 AM

Thanks for your answer. I do not know if you are somehow related to the forum management but it looks like mail notifications may have changed after last move, I did not get your answer on my box.

 

So, please correct me if I am wrong: units are whatever I write in the unit field for each variable. They actually do not mean anything to the PLC unless they belong to one of the predefined units and if that is the case, the corresponding led is lit.

 

To show working hours, I could define a Status variable and perform some logic to keep it below 9999, something like this

 

displayhours.jpgI have not used TDVA´s unless for reference, but since they mean "Tested and validated" a small error is there because what is shown on the menu is the EEPROM variable, which will eventually go higher than 9999. 

 

tdva.jpg

 

I also found that the OverWriteLocalDisplay function expects a DINT number on the third field but filling it with something bigger than 9999 also throws the Outr error on the display.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of