Hi all,
I'm using the M172PDG18R.
If I using a Modbus RTU client, I can see from the M172 side that the client is correctly communicating by using the 'sysMODBUS_msg_received_RS485_1' parameter.
Is there a similar feature, or another method I can use for observing the Modbus TCP interface when the M172 is a server?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-15 05:45 AM
HI,
I don't think we have this same Modbus status variable in TCP.
However, as a:
- Client you can use the System Varaible "sysMbMTcpNodeStatus" to have information on the Modbus TCP communictaion Status.
- Server you have the Variables "sysMbSTcp_SocketServerInfo"
BR
;
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-15 05:45 AM
HI,
I don't think we have this same Modbus status variable in TCP.
However, as a:
- Client you can use the System Varaible "sysMbMTcpNodeStatus" to have information on the Modbus TCP communictaion Status.
- Server you have the Variables "sysMbSTcp_SocketServerInfo"
BR
;