Error reading parameter 20048 - 20061 of M172 HVAC

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Error reading parameter 20048 - 20061 of M172 HVAC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Captain FedericoM Captain
96
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
56
M_Cervati
M_Cervati Support
17
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
Start a Topic
HOANGTHINH
Lieutenant JG HOANGTHINH
Lieutenant JG

Posted: ‎2019-06-03 07:20 PM . Last Modified: ‎2020-09-10 12:57 AM

1 Like
6
4204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-06-03 07:20 PM . Last Modified: ‎2020-09-10 12:57 AM

Error reading parameter 20048 - 20061 of M172 HVAC

Hi all,

  I have a problem when I refresh page to read parameter of TM172, but it fail.

Who can help me ?

 

Picture1.png

 

Thanks for watching

Labels
  • Labels:
  • HVAC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Omaelk
Janeway Omaelk
Janeway

Posted: ‎2019-06-11 12:29 AM

1 Like
2
4194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-06-11 12:29 AM

@MaPundir , you may be able to help @HOANGTHINH ? 😉

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

sesa471789_brid
Ensign sesa471789_brid Ensign
Ensign

Posted: ‎2019-06-13 03:19 AM

In response to Omaelk
1 Like
1
4185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-06-13 03:19 AM

Hello ,

 

Please raise a bfo case with program backup and the firmware of the M172P , As this not a known issue and we have to check and analyis the same.

 

Best Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-06-22 01:38 AM

In response to sesa471789_brid
0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-22 01:38 AM

Hello the register address 20048 is in the range of the standard  EEPROM values.

The EEPROM values on TM172 could be in the range of 16384...20479.

Please check if you have values in this range and check which typ you have defined.

Maybe this could help to anayse the problem. 

Additional an information about the used ESME HVAC Version and BIOS Version could be helpfull.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JacobJ
Crewman JacobJ
Crewman

Posted: ‎2022-07-04 10:34 PM . Last Modified: ‎2022-07-05 09:13 PM

0 Likes
1
2190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-04 10:34 PM . Last Modified: ‎2022-07-05 09:13 PM

I am facing same issue I don't know what to do will you guys help me to solve

Subway Live IQ Login

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-07-04 10:38 PM

In response to JacobJ
0 Likes
0
2187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-04 10:38 PM

It is still necassary to knwo the target version which you select in your application, and to know which version is on the controller. Furthermore it would be important to know if you have EEPROM values in the range which generate the error.

 

WIthout this information it will be hard to solve the problem.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Violet
Violet
Cadet

Posted: ‎2023-05-06 01:15 AM

0 Likes
0
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-06 01:15 AM

I read this article. I think You put a great deal of exertion to make this article. I like your work.

 

Subway Live IQ

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore