Hi Guys,
I'm trying to read modbus registers with M172 as a master by following the below instructions:
Training M172 - M9.3 Modbus Serial Master - YouTube
I am getting '2' as output which is not part of what is described in object properties. I tried clicking the function block in case it shows the source code but no luck.
What does '2' means in this case? Could you please provide a direction where I can find more information?
Thank You.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 12:10 AM
Hi,
I´m not sure but I expect this is a illegal address error. Did you try to increase/decrease the start address with 1?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 12:10 AM
Hi,
I´m not sure but I expect this is a illegal address error. Did you try to increase/decrease the start address with 1?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 12:12 AM
Hi @POPE3909 ,
If we follow the object properties for the "sysMbMTCP_FCxx" it looks like that the number 2 means "Exception code illegal data address" but i am not 100% sure if it is that in your case.
Best regards,
LeTomas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 12:17 AM
Hi Guys,
Thank for your replies. Yes, I was reading the incorrect address. I changed to the correct address and it is all good now.
But I still want to know where/how to check the object properties? In the software, it only shows the following:
No mention of '2'?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 12:28 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 01:01 AM
Hi Pope3909,
it seems there is space to increase the detail on the description.
The response which is fully described on the newer Modbus TCP functions is identical to the standart modbus response which you could find here Link
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2023-05-10 04:06 PM
Thanks guys. 🙏
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of