A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-06 12:00 AM
Hi,
How I can get information about no communication with Modbus TCP slave (1)?
I want that signal to add red crosses on HMI informing that the displayed variables are not up to date.
I using Machine Expert V2.1 and TM251MESE
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-06 03:22 AM
HI @pawel_kowalski_ ,
In Machine Expert if you are using the Ioscanner you can check the Healthbits like this
You can always have a bit blinking on the PLC side and if it does not change the value you can trigger an alarm in the HMI or use a variables that in increasing his value.
If you want to avoid this you can create a variable in the HMI that checks the statistic of the communication using the address "@sys:2" if you get the 1 it means no connection to the device.
I hope this can help you and if this solves the problem remember to put the comment as solution 🙂
Best regards,
LeTomas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-06 03:22 AM
HI @pawel_kowalski_ ,
In Machine Expert if you are using the Ioscanner you can check the Healthbits like this
You can always have a bit blinking on the PLC side and if it does not change the value you can trigger an alarm in the HMI or use a variables that in increasing his value.
If you want to avoid this you can create a variable in the HMI that checks the statistic of the communication using the address "@sys:2" if you get the 1 it means no connection to the device.
I hope this can help you and if this solves the problem remember to put the comment as solution 🙂
Best regards,
LeTomas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-08 11:51 AM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.