Check communication with Modbus TCP Slave

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Check communication with Modbus TCP Slave
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
87
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
55
LeTomas
Lt. Commander LeTomas Lt. Commander
14
M_Cervati
M_Cervati Support
11
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
pawel_kowalski_
Commander pawel_kowalski_
Commander

Posted: β€Ž2023-06-06 12:00 AM

0 Likes
2
2018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-06-06 12:00 AM

Check communication with Modbus TCP Slave

Hi,

 

How I can get information about no communication with Modbus TCP slave (1)?pawel_kowalski__0-1686034313500.png
I want that signal to add red crosses on HMI informing that the displayed variables are not up to date.


I using Machine Expert V2.1 and TM251MESE

 

Labels
  • Labels:
  • Modicon M2xx
  • Tags:
  • english
  • Machine Expert
  • TM251MESE
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: β€Ž2023-06-06 03:22 AM

0 Likes
1
2007
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-06-06 03:22 AM

HI @pawel_kowalski_ ,

 

In Machine Expert if you are using the Ioscanner you can check the Healthbits like this

DiagnosticsIoscanner.PNG

 

You can always have a bit blinking on the PLC side and if it does not change the value you can trigger an alarm in the HMI or use a variables that in increasing his value.

 

If you want to avoid this you can create a variable in the HMI that checks the statistic of the communication using the address "@sys:2" if you get the 1 it means no connection to the device.

syshmi.png

 

I hope this can help you and if this solves the problem remember to put the comment as solution πŸ™‚

 

Best regards,

 

LeTomas

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: β€Ž2023-06-06 03:22 AM

0 Likes
1
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-06-06 03:22 AM

HI @pawel_kowalski_ ,

 

In Machine Expert if you are using the Ioscanner you can check the Healthbits like this

DiagnosticsIoscanner.PNG

 

You can always have a bit blinking on the PLC side and if it does not change the value you can trigger an alarm in the HMI or use a variables that in increasing his value.

 

If you want to avoid this you can create a variable in the HMI that checks the statistic of the communication using the address "@sys:2" if you get the 1 it means no connection to the device.

syshmi.png

 

I hope this can help you and if this solves the problem remember to put the comment as solution πŸ™‚

 

Best regards,

 

LeTomas

Reply

Link copied. Please paste this link to share this article on your social media post.

pawel_kowalski_
Commander pawel_kowalski_
Commander

Posted: β€Ž2023-06-08 11:51 AM

In response to LeTomas
0 Likes
0
1991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-06-08 11:51 AM

Hi,

 

Thanks, @LeTomas  for the answer, I used the method with Healthbits, and that is great for me πŸ‘.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore