Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84599members
353867posts

Cannot connect to M241 over ethernet

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

Solved
MedSelmi
Crewman
Crewman
0 Likes
3
400

Cannot connect to M241 over ethernet

Hello!

I unboxed new TM241CE24T/U and I upgraded Firmware to v5.1.9.21 for using with machine expert v2.0.

My problem is that I can connect to PLC over USB but not over Ethernet, even I can ping to its IP Address and I can access to Plc over web page. 

Can You help me please ?

m241.png

Tags (1)

Accepted Solutions
LeTomas
Lieutenant Lieutenant
Lieutenant

Re: Cannot connect to M241 over ethernet

Hi @MedSelmi ,

 

If you are trying to connect to the M241 via ethernet or USB it is important that the gateway is activated.

 

In the case of the Ethernet connection I always add the device ip address in the "Statis Remote Connections" like this:

 

 

IMAGE_Gateway.png

The device it is shown as "Connected as client".

 

Verify also that your laptop/pc is in the same network as the controller.

 

Best regards,

 

Letomas

See Answer In Context

Tags (1)
3 Replies 3
KJBER
Crewman
Crewman
0 Likes
0
388

Re: Cannot connect to M241 over ethernet


Try IP Adress via NAT (Remote TCP) with port 1105.


 

Tags (1)
LeTomas
Lieutenant Lieutenant
Lieutenant

Re: Cannot connect to M241 over ethernet

Hi @MedSelmi ,

 

If you are trying to connect to the M241 via ethernet or USB it is important that the gateway is activated.

 

In the case of the Ethernet connection I always add the device ip address in the "Statis Remote Connections" like this:

 

 

IMAGE_Gateway.png

The device it is shown as "Connected as client".

 

Verify also that your laptop/pc is in the same network as the controller.

 

Best regards,

 

Letomas

Tags (1)
MedSelmi
Crewman
Crewman
0 Likes
0
357

Re: Cannot connect to M241 over ethernet

Thank you for your support! it's working.

Tags (1)