Cannot connect to M241 over ethernet

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

Solved
MedSelmi
Crewman
Crewman
0 Likes
3
395

Cannot connect to M241 over ethernet

Hello!

I unboxed new TM241CE24T/U and I upgraded Firmware to v5.1.9.21 for using with machine expert v2.0.

My problem is that I can connect to PLC over USB but not over Ethernet, even I can ping to its IP Address and I can access to Plc over web page. 

Can You help me please ?

m241.png

Tags (1)

Accepted Solutions
LeTomas
Lieutenant Lieutenant
Lieutenant

Re: Cannot connect to M241 over ethernet

Hi @MedSelmi ,

 

If you are trying to connect to the M241 via ethernet or USB it is important that the gateway is activated.

 

In the case of the Ethernet connection I always add the device ip address in the "Statis Remote Connections" like this:

 

 

IMAGE_Gateway.png

The device it is shown as "Connected as client".

 

Verify also that your laptop/pc is in the same network as the controller.

 

Best regards,

 

Letomas

See Answer In Context

Tags (1)
3 Replies 3
KJBER
Crewman
Crewman
0 Likes
0
383

Re: Cannot connect to M241 over ethernet


Try IP Adress via NAT (Remote TCP) with port 1105.


 

Tags (1)
LeTomas
Lieutenant Lieutenant
Lieutenant

Re: Cannot connect to M241 over ethernet

Hi @MedSelmi ,

 

If you are trying to connect to the M241 via ethernet or USB it is important that the gateway is activated.

 

In the case of the Ethernet connection I always add the device ip address in the "Statis Remote Connections" like this:

 

 

IMAGE_Gateway.png

The device it is shown as "Connected as client".

 

Verify also that your laptop/pc is in the same network as the controller.

 

Best regards,

 

Letomas

Tags (1)
MedSelmi
Crewman
Crewman
0 Likes
0
352

Re: Cannot connect to M241 over ethernet

Thank you for your support! it's working.