Xenta Server wiring and pin outs
  • Xenta Server wiring and pin outs
‎2018-09-07 02:26 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 03:30 AM
What is the wiring for the RS-232 A, RS-232 B, RS-485 A, RS-485 C, and 10Base-T ports on a Xenta Server?
Satchwell MicroNet, TAC INET, TAC Vista
  • Xenta Servers
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913
  • BACnet/IP
  • BACnet MS/TP
  • M-Bus
  • C-Bus
  • Lon
  • Modbus
The wiring and pin outs for the Xenta Server hardware is detailed in chapter 2.1.2 of the TAC Xenta 500/700/911/913 Product Manual .
The ports and wiring is unique for each port.
RS-232 A port
For serial communication it is typical to only connect the RX, TX, and Ground pins.
Pin 3 4 5
Serial Cable RX TX Ground
 RS 232 B port
10 Base-T port (Web connection)
Note: The Xenta 913 also supports BACnet/IP and Modbus TCP/IP on this port.
RS 485 A port (Modbus)
Note: The Xenta 913 also supports BACnet MS/TP on this port.
If two wire communication is being used then only use pins 5 and 6.
Pin 5 6
If four wire communication is being used then all four pins will be used.
Pin 5 6 7 8
  TX + TX - RX + RX -
RS485 C port (I/NET)
This port is used for I/NET communication.
Pin 19 20
Labels (3)
  • Satchwell MicroNet
  • TAC INET
Tags (2)
  • 4994
  • Pin Outs