Xenta 700 Menta Object Values report [Invalid Address] in Workstation, Read operation failed
  • Xenta 700 Menta Object Values report [Invalid Address] in Workstation, Read operation failed
  • Cody_Failinger
    Cody_Failinger
‎2018-09-10 01:13 AM
Public values, inputs and outputs of a Menta object defined in a Xenta 700 XBuilder project are displaying their values in Workstation as [Invalid Address]. When the value is double- clicked, the following error appears:
Error in property Value.
Read operation failed.
TAC Vista
  • Vista Workstation
  • Xenta Servers
  • Xenta 701, 711, 721, 731
  • XBuilder
  • Menta
The Menta object is not connected to a task. Therefore the Menta application is not being executed.
  1. In XBuilder, generate the project.
  2. Check the output window Generate tab for a warning that states "This Menta Object is not connected to a task"
  3. Double click the warning. The offending Menta object is highlighted.
  4. Drag and drop the Menta object into a Control Task folder in the Network Pane > TAC_Xenta_7xx > Control Tasks
  5. Regenerate and send the project to target. Menta object values should now report valid values.