WorkPlace Commissioning Tool UDP Port: "A critical error occurred in the communication server rtmonitor.exe"
  • WorkPlace Commissioning Tool UDP Port: "A critical error occurred in the communication server rtmonitor.exe"
  • sesa116871
    sesa116871
  • CraigEl
    CraigEl
  • sesa116868
    sesa116868
‎2018-09-07 01:27 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:58 PM
In WorkPlace Commissioning Tool, the following error message appears when browsing a BACnet/IP network: "A critical error occurred in the communication server rtmonitor.exe. Please shutdown this application and the communication server then try again."
TAC IA Series
There could be a Niagara R2 station running on the computer configured for BACnet/IP. Since the Niagara station also uses UDP port 47808 by default, the Niagara service prevented WorkPlace Commissioning Tool from "binding" to the UDP port.
There are two ways to resolve this issue:
  1. Disable the Niagara service when using the WorkPlace Commissioning Tool
  2. In Workplace Pro, stop the station that has the BACnet/IP service enabled, and configure it so that it does not auto-start.
NOTE: If this procedure does not correct the issue and the WorkPlace Tech Tool software is being run on the Windows 7 operating system, refer to WorkPlace Commissioning Tool Windows 7: "A critical error occurred in the communication server rtmon... for information on how to correct what may be a program security settings issue.