VisiSat Version 2.1 Build 196 – Service Pack 1 & 2 Overview

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • VisiSat Version 2.1 Build 196 – Service Pack 1 & 2 Overview
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3024 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

VisiSat Version 2.1 Build 196 – Service Pack 1 & 2 Overview

Picard Product_Support
‎2018-09-11 07:50 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 09:22 PM

Issue

Multiple defects were identified in VisiSat 2.1 Build 196, affecting functionality, export reliability, character encoding, and memory management. These issues impacted integration with StruxureWare Building Operation and the handling of MicroNet engineering files.

Product Line

Satchwell MicroNet

Environment

Satchwell VisiSat 2.1 build 196

Cause

  • Legacy limitations in character handling and export formatting
  • Improper object disposal during export routines
  • Encoding mismatches for non-ASCII characters
  • Incomplete validation logic for interface exports
  • Lack of error handling for blank point lists

Resolution

Service Pack 1 (Build 200)

Fixes Included:

  1. ARCnet Debug Tool

    • Property editor now functions correctly in the ARCnet debug Excel spreadsheet. (Defect 1633)
  2. Export Enhancements

    • Point names now support up to 32 characters; descriptions up to 50 characters. (Defect 1706)
  3. MicroNet Interface Handling

    • MicroNet Interfaces are no longer exportable/importable via StruxureWare WorkStation.
    • All engineering must be completed in VisiSat before import. (Defect 1765)
  4. Point List Stability

    • Blank point lists can now be saved without triggering errors. (Defect 1784)
  5. Memory Leak Fix

    • Exporting to StruxureWare no longer causes memory leaks. (Defect 1808)

Installation Instructions:

  • Ensure VisiSat 2.1 Build 196 is installed.
  • Download and apply Service Pack 1.
  • Note: Control Panel may still display build as 2.1.196 after installation.

Service Pack 2 (Build 201)

Fixes Included:

  1. Character Encoding Correction

    • Non-ASCII characters in import files are now correctly converted. (Defect 31467)
  2. Alarm and Trend Point Import

    • Points with alarms and trends are now properly included in import files.

Installation Instructions:

  1. Ensure Service Pack 1 is already installed.
  2. Shut down VisiSat and VisiSat-Server.
  3. Run VisiSat 2.1.196 Service Pack 2.exe.
  4. Extract to the VisiSat installation root (or extract elsewhere and move the Satchwell folder to C:\).
  5. When prompted to replace existing files, select "Yes to All".
  6. Restart VisiSat.
  • After installation, build number updates to 2.1.201, but may still appear as 2.1.196 in Control Panel.

  • Download Service Pack 2.

Labels (1)
Labels:
  • Satchwell MicroNet
Attachments
VisiSat 2_1_200 (2.1.196 SP1).zip
VisiSat 2_1_201 (2.1.196 SP2).zip
Tags (3)
  • Find more articles tagged with:
  • 16251
  • CraigEllis25
  • iacs
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore