Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Using lontool32 to download a stand-alone controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using lontool32 to download a stand-alone controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2682 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using lontool32 to download a stand-alone controller

Picard Product_Support
‎2018-09-07 07:39 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:09 PM

Issue

A stand-alone Xenta programmable controller can have an application downloaded into it using a serial cable and Menta. However, if that base unit has additional Xenta 400 I/O modules associated with it, they will never recognize and associate with their base controller.

Product Line

TAC Vista

Environment

  • Stand-Alone Xenta Programmables
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Xenta 400 I/O Modules
  • Menta

Cause

A direct download of a Menta application does not download any network description information along with it (.ndb file) -- it is application only.  The controller can be downloaded via System Plug-in, which places the .ndb file into the controllers, but this requires the creation of a "dummy" network.  lontool32 offers a quick work around for truly stand-alone controllers.

Resolution

It is best to use the most current system program for this method as older versions may not work. Note: While Menta allows for configuration of the communications port from COM1 to COM9, lontool32 can only communicate on COM1. Follow the instructions in Reassigning a USB Serial Adaptor to a desired COM port to force the hardware to COM1. Then launch the Menta Setup tool from the Start Menu (Start >All Programs > Schneider Electric > TAC Tools X.X.X > Menta Setup) and set the Com Port to 1.

  1. Using Menta, create and download your .MTA file to the Xenta programmable using the direct connect method. This connection will also be used for lontool32 downloads.
  2. After Downloading, ensure Menta is "offline" to allow lontool32 an active connection on COM1.
  3. Open the lontool32 program which is located in your Menta program folder (e.g. C:\Program Files\Schneider Electric\TAC Menta 5.X.X\lontool32.exe)
  4. In lontool32, select the add button to add group, then select add node to add Base Unit.
  5. Double click on the Base unit to edit the node in the Network Configuration window.
  6. Select the Upload button to retrieve the Device and associated  I/O information. You will see this information populate the "database" column and associated I/O will populate the "I/O Modules" window below.
    *If the upload button remains grayed out, Ensure the Menta connection is "Offline" or follow the instructions here Reassigning a USB Serial Adaptor to a desired COM port to force the hardware to COM1. Also, check in the TAC Menta Setup program to verify that the Com Port is set to 1.
  7. Edit each I/O module by right clicking and selecting "Edit I/O".
    1. Use the "Service Pin" button to set the Neuron ID . 
    2. Enter the Subnet and a unique Node address in the appropriate text boxes.
    3. Repeat this procedure for every base unit in the network. If the network will contain more than one Base Unit, one must be designated as master by selecting the "master" check box in the Network Configuration window.
  8. When all the I/O has been updated, Select the "Download" button to generate and send the .NDB file to the base unit.
  9. Your I/O Modules should now be online which can be verified by the status light now oscillating every second vs. flashing quickly.
  10. If the Subnet Node information populates to a 0, you must type a subnet address and unique Node address for each unit on the network.  
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4025
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of