Troubleshooting AS configuration issues with IP address

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting AS configuration issues with IP address
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • sesa139513
    sesa139513
  • Derrick_Ratliff
    Derrick_Ratliff
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9753 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting AS configuration issues with IP address

Picard Product_Support
‎2018-09-06 12:03 PM

Last Updated: Picard RobertAndriolo Picard ‎2022-04-04 04:32 PM

Issue

Default IP Address for AS,TCP/IP IPv6, and StruxureWare Building Operation

Product Line

EcoStruxure Building Operation

Environment

Building Operation site

Cause

Attempted to ping AS and got "Request timed out." (AS does not have a default IP address)

After going through StruxureWare Building Operation Device Administrator's Open Console which is also referred to as PuTTY(outlined below #1), the configuration has the proper:

  • Hostname
  • DHCP enabled/disabled
  • IP address
  • Subnet mask
  • Default gateway
  • DNS server
  • Domain name

Still the ping of the AS IP address receives "Request timed out" 

Is this from a Virtual environment? See Resolution 6 below.

Resolution

Check the following settings:

  1. Use Device Administrator to set a static IP address for an Automation Server.
    DeviceAdmin.png
    1. Connect the Automation Server to the PC's USB port
    2. In Device Administrator, select the Automation Server you want to set the IP address for.
    3. On the View menu, click Console which opens console or PuTTY.  See NOTE below if Console icon not shown.
    4. If you are prompted to type a login name, default is "admin". Press Enter.
    5. If you are prompted to type a password, default is "admin". Press Enter.
    6. Type "setip". Press Enter.
    7. If you want to change the host name, delete the current host name and type a new host name. Press Enter.
    8. Type "no" to use a static IP address. Press Enter.
    9. Type the IP address for the Automation Server. Press Enter.
    10. Type the subnet mask. Press Enter.
    11. Type the default gateway address. Press Enter.
    12. Type the DNS server address. Press Enter.
    13. Type the domain name. Press Enter.
    14. Type "yes" to write the configuration. Press Enter.
    15. After the Network settings, "successfully updated" message is displayed,
    16. Type "exit" to log off. Press Enter.

  2. Rather than connect through a router or switch, plug the Ethernet cable directly into the AS. Ethernet port is AutoSensing (No Crossover Cable required).

  3. Adjust IP settings to close proximity IP and Subnet, such as the following example:
    1. Computer IP=192.168.1.2
    2. Computer Subnet=255.255.255.0
    3. Automation Server IP=192.168.1.5
    4. Automation Server Subnet=255.255.255.0

  4. Have only one NIC or network card enabled in Network Settings on this computer

  5. In Network Settings, uncheck the Internet Protocol Version 6 (TCP/IPv6), which will disable. TCP/IP Version 6 is the latest version of the internet protocol which provides communication across diverse interconnected networks which is not necessary for this configuration.

  6. If you are using a virtual environment, exit that virtual environment and attempt the configuration from the real-world environment. 

  7. If AS hangs or comes up with the Status light in red:
    1. Start Device Administrator and establish a USB connection between the computer and AS.
    2. Press the reset button on the AS three times in a row to place it in DFU mode.
    3. The AS will disappear from the Device Administrator and re-appear in DFU mode.
    4. Perform Upgrade device operation.

  8. The AS can be configured using DHCP (Dynamic Host Configuration Protocol) using Device Manager. It is recommended to not use DHCP but rather Static IP addresses. If the IP of the AS/ES changes, then reconfiguration of other AS/ES, or BACnet/IP, Modbus/IP interface needs to be changed also.

NOTE: Beginning with StruxureWare Building Operation release 1.4.0, the Device Administrator no longer displays the "Console" icon on its toolbar. You can still access the PuTTY console by holding down the shift key and right-clicking on the automation server. You will have the option to open 'Console'.

NOTE: Some network configuration setting changes may be prevented by the connected network. If you have issues getting the AS to save changes, disconnect the AS from the ethernet and use the USB connection only.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 11216
  • RobertAndriolo22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore