Set up a two wire LTS80 Lini-Temp sensor on a 7756 PCU on the upper board
  • Set up a two wire LTS80 Lini-Temp sensor on a 7756 PCU on the upper board
‎2018-09-06 11:01 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:59 AM
TAC INET
  • LTS80 Lini-Temp temperature sensor
  • 7756 PCU upper board
Lini-temp is a type of temperature sensor that is compatible with the I/NET product line.
  • For Fahrenheit:
    • m = 0.21978
    • b = -459.6
  • For Centigrade:
    • m = 0.1221
    • b = -273.0
  • J22 to 15 VDC
  • 10k ohm resistor in slot "A"
  • Remember, the lower board has a different resolution than the upper board. See Set up a two wire LTS80 Lini-Temp sensor on a 7756 PCU on the lower board for details on the lower board.
  • Refer to TCON 127: 7756 PCU Installation Guide for details
  • TAC INET
  • 1100