Set up a two wire LTS80 Lini-Temp sensor on a 7756 PCU on the lower board
  • Set up a two wire LTS80 Lini-Temp sensor on a 7756 PCU on the lower board
‎2018-09-06 11:03 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:59 AM
TAC INET
  • LTS80 Lini-Temp temperature sensor
  • 7756 PCU lower board
Lini-temp is a type of temperature sensor that is compatible with the I/NET product line.
  • For Fahrenheit:
    • M = 0.0274669
    • B = -459.8
  • 10k ohm resistor in slot "A"
  • Remember, the lower board has a different resolution than the upper board. See Set up a two wire LTS80 Lini-Temp sensor on a 7756 PCU on the upper board for details on the upper board.
  • Refer to TCON 127: 7756 PCU Installation Guide for details
  • TAC INET
  • 1101