Menta Parser Errors

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Menta Parser Errors
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3723 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Menta Parser Errors

Picard Product_Support
‎2018-09-07 03:26 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:12 PM

Issue

There are 31 different Parser Errors that can result from a Menta direct download to a programmable controller.

Product Line

TAC Vista

Environment

  • Xenta programmables
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Menta

Cause

Causes vary by error code.  See details below and any links to additional information.

Resolution

No. Name Comment
0 PARSER_OK  
1 PARSER_CREATE_OBJ_ERROR Seen immediately on an attempt to download directly.  Subsequent attempts result in "Download Failed."  Resetting the device caused the error to come back.  See in the error in COD window that its showing 0,0 coordinate pairs and underlying information.  The error's not in the Menta code itself.  No spaces allowed in the Program Specification -- a change from earlier versions.  May render your device unusable after attempting to download -- correct files won't download either.
2 PARSER_ALLOCATE_FLASH_ERROR  
3 PARSER_IOMOD_SAVE_ERROR  
4 PARSER_VERSION_ERROR  
5 PARSER_APPNAME_ERROR  
6 PARSER_ABBREV_ERROR  
7 PARSER_TYPE_ERROR  
8 PARSER_SOURCEFILE_ERROR  
9 PARSER_SIGNAL_ERROR Error 9 has to do with the signal list (ESP-file) there all the public signals are transferred from Menta into the GraphOP tool by a sort of a long list. Normally, if you just make the application in Menta, this should not be any problem, however search and replace on signal names could give you headache.
10 PARSER_ALARMTEXT_ERROR Seems to download and fails on resetting device.  Had a case where this occurred when the application was too large due to generation of an OP tree where there wasn't one before.  Check memory.
11 PARSER_TIMESCHEDULE_ERROR  
12 PARSER_IOMOD_ERROR  
13 PARSER_IO_ERROR The terminal may not exist in this unit type.  Could also include situations where the same terminal reference is used in multiple references (this could be on the Xenta or the IO module). Typically caused by copy/paste.
Reference to unsupported I/O Error in COD file - Error:13 for more information.
14 PARSER_CYCLETIME_ERROR  
15 PARSER_CODE_ERROR Constants table has scientific notation, PVR blocks have scientific notation, Expression block attempting to use scientific notation, application size too large
PARSER_CODE_ERROR Error in COD file - Error:15 for more information.
16 PARSER_DST_ERROR  
17 PARSER_CHECKSUM_ERROR  
18 PARSER_EOF_ERROR  
19 PARSER_SNVT_ERROR  
20 PARSER_SNVT_CRC_ERROR  
21 PARSER_AUTHOR_ERROR  
22 PARSER_BLUEPRINT_ERROR  
23 PARSER_NO_BPR_FILE  
24 PARSER_TLOG_RAM_ERROR  
25 PARSER_TLOG_FLASH_ERROR  
26 PARSER_TLOG_TO_MANY  
27 PARSER_TLOG_ERROR_IN_DEF  
28 PARSER_TOLG_PARSE_ERROR  
29 PARSER_IMAGE_TOO_BIG  
30 PARSER_RESET_BEFORE_PARSED  
31 PARSER_SELF_DESTRUCTION_PERFORMED  
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4036
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore