Mail Service in a Niagara R2 UNC station configured correctly but e-mails not being sent to the SMTP server
  • Mail Service in a Niagara R2 UNC station configured correctly but e-mails not being sent to the SMTP server
  • Cody_Failinger
    Cody_Failinger
  • sesa119747
    sesa119747
  • sesa116871
    sesa116871
‎2018-09-06 02:57 PM
The Mail Service in a Niagara R2 UNC station is configured correctly.  However, e-mails do not get sent to the SMTP server.
TAC IA Series
The Niagara station needs to enable mail.smtp.auth in system.properties.
In the station, the following lines need to be added to the system.properties file if authentication is required:
mail.smtp.auth=true
mail.useUTF=false
Once these lines are added and the UNC is re-booted, the UNC will successfully send emails to the SMTP server.
  • TAC IA Series
  • 2656