Issue
How to set the neuron ID of an I/O Module in a Vista classic network.
Product Line
TAC Vista
Environment
- Vista Classic Network
- Xenta I/O modules
Cause
Xenta I/O modules beneath a base unit (300 or 400 series) do not show up in the Folder view tree structure. You cannot right-click and set a neuron ID the same way you do for a base unit.
Resolution
- Click on the Xenta base unit (300 or 400 series controller) in the tree structure.
- This brings up a list of modules inside the Menta file as well as two option modules that cannot be seen from the tree structure-- $IO and $LOGS.
- Double click the $IO module.
- All of the I/O modules defined in the Menta file are listed here. Right-click, properties, to set the neuron ID.