Xenta I/O modules beneath a base unit (300 or 400 series) do not show up in the Folder view tree structure.  You cannot right-click and set a neuron ID the same way you do for a base unit.
  1. Click on the Xenta base unit (300 or 400 series controller) in the tree structure.
  2. This brings up a list of modules inside the Menta file as well as two option modules that cannot be seen from the tree structure-- $IO and $LOGS.
  3. Double click the $IO module.
  4. All of the I/O modules defined in the Menta file are listed here.  Right-click, properties, to set the neuron ID.