Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet 3rd party controller does not respond to Find New BACnet Devices (Who-Is/I-Am) or Device Discovery

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet 3rd party controller does not respond to Find New BACnet Devices (Who-Is/I-Am) or Device Discovery
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • Dave_Shore
    Dave_Shore
  • PaulFr
    PaulFr
  • Carl_Slack
    Carl_Slack
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5913 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet 3rd party controller does not respond to Find New BACnet Devices (Who-Is/I-Am) or Device Discovery

Picard Product_Support
‎2018-09-07 04:25 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-04-18 06:14 AM

Issue

BACnet 3rd party controller will not respond to Find New BACnet Devices (Who-Is/I-Am), so will not come online to Continuum or EBO

Product Line

EcoStruxure Building Operation, Andover Continuum

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Edge Server - Standard
  • Continuum Cyberstation
  • Continuum bCX4040 (BACnet)

Cause

BACnet MSTP device can be master or slave. BACnet MSTP slave will only respond to a request from a master device, and will not respond to the Who-Is broadcast so it can not be discovered.

  • EBO: EBO does not support slave devices. EBO does not currently have a way to statically configure MAC addresses as it relies on dynamic discovery.
     
  • Continuum: Slave only devices cannot come online.

Resolution

  • Check 3rd party device documentation or contact 3rd party device vendor for Master/Slave settings and configure for Master to communicate on a MSTP network.
  • Use 3rd party interface to convert to a protocol that can be directly supported by EBO or Continuum.

Examples of BACnet MSTP Slaves that are known not to respond to EBO or Continuum Who-Is request and so not come online are:

- The Babel Buster 485XM from Control Solutions Inc is BTL listed as a BACnet Slave device , their PICs statement can be seen Here.

- Wilo pumps Interface Modules: IF-Modul BACnet & IF-Modul Stratos BACnet, their PICs statement can be seen Here.

 

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
Tags (3)
  • Find more articles tagged with:
  • 4420
  • DavidShore21
  • MahmoudSayed23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore