TC900 Thermostat Setpoint Changed by Itself

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • TC900 Thermostat Setpoint Changed by Itself
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
nathanaelowen11
Crewman nathanaelowen11
Crewman

Posted: ‎2024-01-27 12:10 PM

0 Likes
5
1861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-27 12:10 PM

TC900 Thermostat Setpoint Changed by Itself

For the TC900, i found that sometimes the setpoint are changed by itself to 26 degree celcius. Can we prevent this from happening?

Labels
  • Labels:
  • Thermostats
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-01-29 04:38 PM . Last Modified: ‎2024-02-04 03:03 PM

0 Likes
1
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 04:38 PM . Last Modified: ‎2024-02-04 03:03 PM

@nathanaelowen11  the factory default setpoint is 26°C, I suspect that the thermostat is going back to default after power failure. Please ensure that parameter 03 is set to 00

 

 

Refer to the Installation guide for details on accessing these parameters

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-01-29 04:38 PM . Last Modified: ‎2024-02-04 03:03 PM

0 Likes
1
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 04:38 PM . Last Modified: ‎2024-02-04 03:03 PM

@nathanaelowen11  the factory default setpoint is 26°C, I suspect that the thermostat is going back to default after power failure. Please ensure that parameter 03 is set to 00

 

 

Refer to the Installation guide for details on accessing these parameters

Reply

Link copied. Please paste this link to share this article on your social media post.

nathanaelowen11
Crewman nathanaelowen11
Crewman

Posted: ‎2024-02-05 04:59 AM

In response to CraigEl
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-05 04:59 AM

Thank you for your reply. I see the factory default is 26°C. I already ensure the parameter 03 is already set to 00 (since its default value). Is it possible due to power blink? Because in the same project i have another pair of thermostat doing duty-standby FCU by turning off the power supply. Those pair of thermostat is not affected.

The one that is changing is the one standing individually, all over the building (76 units), changed to 26 at the same time.

Reply

Link copied. Please paste this link to share this article on your social media post.

somprasong_rojp
somprasong_rojp Cadet | EcoXpert Master
Cadet | EcoXpert Master

Posted: ‎2024-04-23 11:44 PM

0 Likes
2
1589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-23 11:44 PM

How to set KP, KI from display of TC900 Thermostat.

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-04-24 12:12 AM

In response to somprasong_rojp
0 Likes
1
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 12:12 AM

@somprasong_rojp please contact your local product support who can provide you instructions.

Reply

Link copied. Please paste this link to share this article on your social media post.

somprasong_rojp
somprasong_rojp Cadet | EcoXpert Master
Cadet | EcoXpert Master

Posted: ‎2024-04-24 12:53 AM

In response to CraigEl
0 Likes
0
1580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 12:53 AM

Thank you for your reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore