M800 Forta not working

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • M800 Forta not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
roger_maalouly
Ensign roger_maalouly
Ensign

Posted: ‎2024-04-24 01:49 AM

0 Likes
4
2204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 01:49 AM

M800 Forta not working

Hello

I have an M800 Forta actuator installed to operate as 0-10VDC modulating

We have connected 24VAC power on G and G0

We have connected the 0-10VDC cable from the controller on X1 and XM

I have set all the dip switches in the correct position for this purpose (All the switches are OFF)

The actuator is not rotating at all. I modulated the signal with different values between 0 and 10 VDC, but still not operating.

I even tried to short-circuit the VH and VC to G0, without any result

Knowing that in the manual position, the actuator rotates without any obstruction

I have attached some pictures

Please how can I assess the problem, it is a wrong connection or it is an actuator defect?

 

 

Attachments
Labels
  • Labels:
  • Traditional Valves and Actuators
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-04-25 05:05 PM

In response to roger_maalouly
0 Likes
0
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 05:05 PM

@roger_maalouly it sounds like a faulty actuator, contact your local support team for the next steps

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-04-24 05:16 AM

0 Likes
2
2180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 05:16 AM

@roger_maalouly have you toggled DIP switch 9 from OFF to ON and back to OFF with the actuator connected to the valve, this sets the actuator into calibration mode and it will move to both ends of it's travel and set it's stroke range. If this is not done the actuator will not respond the the voltage input signal.

 

See page 12 of the Installation Instructions for further information.

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_maalouly
Ensign roger_maalouly
Ensign

Posted: ‎2024-04-24 10:57 PM

In response to CraigEl
1 Like
1
2156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 10:57 PM

@CraigEl We have toggled DIP switch 9 from OFF to ON and back to OFF as you mentioned, but still not working. It did not react as it is supposed to do. Actually it did not move at all

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-04-25 05:05 PM

In response to roger_maalouly
0 Likes
0
2138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 05:05 PM

@roger_maalouly it sounds like a faulty actuator, contact your local support team for the next steps

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_maalouly
Ensign roger_maalouly
Ensign

Posted: ‎2024-04-25 11:05 PM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 11:05 PM

@CraigEl Thank you for your support

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore