Suitable duct mountable temperature sensor for TC-300 (Except RS- 03)
Is there any other duct mountable temperature sensor that can is compatible with TC- 300 (other than the RS-03)?
I have found that STD 500-150 is 10k NTC as RS-03 will it be possible for me to use it with the TC-300?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 08:09 PM
RS-03 and STD500 are both using the NTC10K type3 sensing element, but the component - thermistors of these 2 references are different, it means there is some difference on the character .
Better to do some on-site testing before use it, because different characters(resistance v temperature table) should impact the accuracy performance if connected to TC thermostat.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 08:09 PM
RS-03 and STD500 are both using the NTC10K type3 sensing element, but the component - thermistors of these 2 references are different, it means there is some difference on the character .
Better to do some on-site testing before use it, because different characters(resistance v temperature table) should impact the accuracy performance if connected to TC thermostat.