Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

STR-150 & Return Sensor with Xenta 122-FC

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • STR-150 & Return Sensor with Xenta 122-FC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Intelligent Devices Forum
Start a Topic
digvijay
Lieutenant JG digvijay
Lieutenant JG

Posted: β€Ž2019-09-09 11:31 PM . Last Modified: β€Ž2020-12-02 04:31 AM

1 Like
7
5357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-09-09 11:31 PM . Last Modified: β€Ž2020-12-02 04:31 AM

STR-150 & Return Sensor with Xenta 122-FC

Hi All,

 

I have a scenario in which an STR-150 thermostat and a return sensor are to be connected to a Xenta-122FC. I need to run the Xenta controller based on the return sensor temperature value and setpoint to be given from server. And have to export the temperature & setpoint values from STR-150 to other controller(to be used for other purpose). Does anyone know how to achieve this? Which of the Xenta terminals the thermostat and return sensor should be connected? How should be the bindings be done?

  • Tags:
  • 122FC
  • STR150
  • xenta
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Omaelk
Janeway Omaelk
Janeway

Posted: β€Ž2019-09-10 04:46 AM

1 Like
0
5349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-09-10 04:46 AM

Hello @digvijay , welcome on Exchange community. I add @MikaelKrantz to the thread as he may be able to help you with your issue. 

 

PS: do not hesitate to use the search bar with key words to check if your issue was not already discussed somewhere in the community πŸ˜‰ 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Guinan MikaelKrantz Guinan
Guinan

Posted: β€Ž2019-09-10 06:58 AM

1 Like
5
5345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-09-10 06:58 AM

The TAC Xenta 122-FC device has to be configured with the ZBuilder tool, that is an LNS PlugIn software.

Here you can select what input you should use for the temp, and under Configuration tab, Application, Special Functions, there is a checkbox for selecting Do not use space temperature from STR150.

Reply

Link copied. Please paste this link to share this article on your social media post.

digvijay
Lieutenant JG digvijay
Lieutenant JG

Posted: β€Ž2019-09-10 07:24 AM

In response to MikaelKrantz
1 Like
2
5339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-09-10 07:24 AM

Thanks Mikael! How can I export the STR-150 Temperature and Setpoint values in this situation?
Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Guinan MikaelKrantz Guinan
Guinan

Posted: β€Ž2019-09-10 07:36 AM

In response to digvijay
1 Like
1
5335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-09-10 07:36 AM

Not from the sensor, but from the controller.

nvoSpaceTemp

nvoEffectSetpt

Reply

Link copied. Please paste this link to share this article on your social media post.

digvijay
Lieutenant JG digvijay
Lieutenant JG

Posted: β€Ž2019-09-11 10:33 PM

In response to MikaelKrantz
1 Like
0
5320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-09-11 10:33 PM

Let me check on the site for the values on these NVOs and get back to you. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Waqas_Shahid
Ensign Waqas_Shahid
Ensign

Posted: β€Ž2025-05-26 12:06 AM

In response to MikaelKrantz
0 Likes
1
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-26 12:06 AM

Is there any option for the selection of either STR-150 or temperature sensor once controller is added under SBO under these sub folder as my previous selection in this controller on return sensor now I want to replace it with STR-150 and I don't have LNS or Tac vista.

1000184332.jpg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Guinan MikaelKrantz Guinan
Guinan

Posted: β€Ž2025-05-26 12:53 AM

In response to Waqas_Shahid
0 Likes
0
1604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-26 12:53 AM

What type of controller du you have?

STR150 only talk to the TAC Xenta 100 series.

Or, do you think about STR350, which are using SNVT?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore