SP90 Actuator Firmware

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • SP90 Actuator Firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
37
Troy_Wecker
Lieutenant JG Troy_Wecker Lieutenant JG
11
Gary
Gary Schneider Alumni (Retired)
11
MikaelKrantz
Kirk MikaelKrantz Kirk
11
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Solved
MohanR
Ensign MohanR Ensign
Ensign

Posted: ‎2024-08-06 01:04 AM

0 Likes
8
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-06 01:04 AM

SP90 Actuator Firmware

Hi,  

 

We experienced issues due to third party contractor who had labelled supply/return piping incorrectly on some of the FCU's that caused issue for Supply temp sensor connected to T1 & Return temp sensor connected to T2 (instead of vice a versa) by SE contractor.

 

As its hard to access some of these FCU's (to swap these supply/return air temp sensors), need firmware that would allow to swap from software.  The current SP90 are with Revision no 4.21.   

 

I believe there was new firmware of SP90 to be launched (probably last year) which would have functionality to swap T1 and T2 inputs from software/frontend. 

 

Is there firmware available that would allow to swap remotely? 

 

On upgrading firmware:

1. Would it change any of parameters? 

2. Would new firmware will introduce any additional points?

 

Above questions as currently we have points onboarded on BDP and any additional points introduced due to new firmware would affect BDP hence need to know before upgrading firmware.

 

Thanks for your kindest support in advance.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Simon_Firth
Lieutenant JG Simon_Firth Lieutenant JG
Lieutenant JG

Posted: ‎2024-08-09 03:44 PM

0 Likes
6
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-09 03:44 PM

Hi Mohan (and Craig)

We do have a firmware update file which directly resolves T1 and T2 temperature probes being installed the opposite way around to the instructions.

Essentially, two key new objects are introduced which enable the temperature sensors to be swapped.

MSV:42 (T1 input) and MSV:43 (T2 input).  For both you are able to select each as:

1: Disabled
2: Supply temperature
3: Return temperature

 

I am not able to upload the firmware files to this site so I will add them to our sharepoint

New Firmware and Widget.

Please use file V439 for actuators using 4.21 firmware (products marked V1xxx on the product label),

file V539 is for the very latest actuators (products marked V2xx on the product label)

 

Simon

Mr Valve

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-08-06 01:18 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-06 01:18 AM

@Simon_Firth are you aware of any SP90 firmware that can address this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Simon_Firth
Lieutenant JG Simon_Firth Lieutenant JG
Lieutenant JG

Posted: ‎2024-08-09 03:44 PM

0 Likes
6
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-09 03:44 PM

Hi Mohan (and Craig)

We do have a firmware update file which directly resolves T1 and T2 temperature probes being installed the opposite way around to the instructions.

Essentially, two key new objects are introduced which enable the temperature sensors to be swapped.

MSV:42 (T1 input) and MSV:43 (T2 input).  For both you are able to select each as:

1: Disabled
2: Supply temperature
3: Return temperature

 

I am not able to upload the firmware files to this site so I will add them to our sharepoint

New Firmware and Widget.

Please use file V439 for actuators using 4.21 firmware (products marked V1xxx on the product label),

file V539 is for the very latest actuators (products marked V2xx on the product label)

 

Simon

Mr Valve
Reply

Link copied. Please paste this link to share this article on your social media post.

MohanR
Ensign MohanR Ensign
Ensign

Posted: ‎2024-08-12 12:49 AM

In response to Simon_Firth
0 Likes
5
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-12 12:49 AM

Good morning Simon and so kind of you to advise.  Trying to find on how to upgrade firmware remotely...

MohanR_0-1723448954251.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-08-12 04:53 PM

In response to MohanR
0 Likes
4
925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-12 04:53 PM

@MohanR among the files linked by @Simon_Firth is a Word document titled Upgrade_w_SBO that details how firmware can be upgraded using BACnet from EBO. The PDF titled Upgrading multiple units also has instructions on how multiple actuators can be upgraded using an EBO search.

Reply

Link copied. Please paste this link to share this article on your social media post.

MohanR
Ensign MohanR Ensign
Ensign

Posted: ‎2024-08-12 11:31 PM

In response to CraigEl
0 Likes
3
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-12 11:31 PM

Morning Craig,

 

I liaised with Simon via teams yesterday as SP-90s are configured over Modbus via RP-C controller and not via separate MSTP hence there is no way to access SP-90 Application.  As advised, I have escalated with BMS tech support.  Received call from tech support.  Tech support will get back once they find way to upgrade under these circumstances.

 

Attached screenshots FYI.

 

Sincerely appreciate to Simon and Yourself for support.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-08-13 12:04 AM

In response to MohanR
0 Likes
2
909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-13 12:04 AM

@MohanR if you are using modbus then I'm afraid that support won't be able to assist, modbus doesn't support these file transfers and upgrades or at least the current EBO implementation doesn't.

Reply

Link copied. Please paste this link to share this article on your social media post.

MohanR
Ensign MohanR Ensign
Ensign

Posted: ‎2024-08-13 12:12 AM

In response to CraigEl
0 Likes
1
908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-13 12:12 AM

Thanks Craig.  Is there any other alternate way to upgrade else we will have to physically access and swap sensors on field.

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-08-13 12:14 AM

In response to MohanR
0 Likes
0
908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-13 12:14 AM

@MohanR aside from BACnet, none that I'm aware of.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of