SLPSTX2 Room Humidity Sensor Inaccuracy

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • SLPSTX2 Room Humidity Sensor Inaccuracy
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
williamcitrayas
Ensign williamcitrayas
Ensign

Posted: ‎2025-10-12 10:03 PM

0 Likes
3
458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-12 10:03 PM

SLPSTX2 Room Humidity Sensor Inaccuracy

I have installed SLPSTX2 Room Humidity sensor. the controller read the room humidity sensor using Modbus RTU protocol.

The Room Humidity value of SLPSTX2 is inaccurate, the error value from real measurement is about 10%.

I try to offset room humidity value using modbus RTU on address 54 & 55 holding register as shown picture below. but modscan return "invalid repond from modbus query" message.

williamcitrayas_1-1760331633266.png

how to offset the room humidity value of SLPSTX2?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
David_Purser
Picard David_Purser Picard
Picard

Posted: ‎2025-10-14 05:55 AM

0 Likes
1
410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 05:55 AM

Using ModScan, it has to be configured for 32-bit float and not using default settings.

  • Device ID: Enter the Modbus slave address of the SLPSTX2.
  • Function Code: Use 03 for Read Holding Registers.
  • Starting Address: Enter 54.
  • Length: Set to 2 (since 32-bit float spans two 16-bit registers).
  • Display Format:
    • Go to Display → Floating Point.
    • Choose MSRF (Most Significant Register First) or LSRF (Least Significant Register First) depending on the device’s word order.
      • Most devices use MSRF, but if the value looks wrong (e.g., extremely small or large), try LSRF.

Can you reply and correct these instructions, especially the MSRF or LSRF setting you found to work?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

williamcitrayas
Ensign williamcitrayas
Ensign

Posted: ‎2025-10-14 08:51 PM

In response to David_Purser
0 Likes
0
398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 08:51 PM

Thank you for the respond.

I recently contacted the schneider technical support, Turn out that the SLPSTX2 that we used is the old version (Production 2022).

And the version that capable to offset the temperature and the RH is production of 2024 above.

And now the sensor still inaccurate and I can't offset the RH value.

is there any way to improve the accuracy of the RH value of the sensor?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

SantiagoFraile
Ensign SantiagoFraile Ensign
Ensign

Posted: ‎2025-11-13 07:42 AM

0 Likes
0
247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-13 07:42 AM

Hi William, How are you? If your intention is to apply an offset directly on the sensor screen, you’ll need to order a new SLPSTX2, as this feature was introduced at the firmware level (on production plant) in June 2024. Currently, there’s no way to field-upgrade existing SLP units. The only option available on-site today is to apply the EBO offset, as David described.

 

That said, I think the real question is: why are you seeing a 10% RH deviation? Is this sensor installed in an office environment or a different type of application? Remember that Living Space sensors were designed to be used in applications such as: offices, hotels, school, etc. places where environmental airflow is steady. If this is the case, please open a ticket with the support team so they can investigate the sensor’s performance. Rgds.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
David_Purser
Picard David_Purser Picard
Picard

Posted: ‎2025-10-14 05:55 AM

0 Likes
1
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 05:55 AM

Using ModScan, it has to be configured for 32-bit float and not using default settings.

  • Device ID: Enter the Modbus slave address of the SLPSTX2.
  • Function Code: Use 03 for Read Holding Registers.
  • Starting Address: Enter 54.
  • Length: Set to 2 (since 32-bit float spans two 16-bit registers).
  • Display Format:
    • Go to Display → Floating Point.
    • Choose MSRF (Most Significant Register First) or LSRF (Least Significant Register First) depending on the device’s word order.
      • Most devices use MSRF, but if the value looks wrong (e.g., extremely small or large), try LSRF.

Can you reply and correct these instructions, especially the MSRF or LSRF setting you found to work?

Reply

Link copied. Please paste this link to share this article on your social media post.

williamcitrayas
Ensign williamcitrayas
Ensign

Posted: ‎2025-10-14 08:51 PM

In response to David_Purser
0 Likes
0
399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 08:51 PM

Thank you for the respond.

I recently contacted the schneider technical support, Turn out that the SLPSTX2 that we used is the old version (Production 2022).

And the version that capable to offset the temperature and the RH is production of 2024 above.

And now the sensor still inaccurate and I can't offset the RH value.

is there any way to improve the accuracy of the RH value of the sensor?

Reply

Link copied. Please paste this link to share this article on your social media post.

SantiagoFraile
Ensign SantiagoFraile Ensign
Ensign

Posted: ‎2025-11-13 07:42 AM

0 Likes
0
248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-13 07:42 AM

Hi William, How are you? If your intention is to apply an offset directly on the sensor screen, you’ll need to order a new SLPSTX2, as this feature was introduced at the firmware level (on production plant) in June 2024. Currently, there’s no way to field-upgrade existing SLP units. The only option available on-site today is to apply the EBO offset, as David described.

 

That said, I think the real question is: why are you seeing a 10% RH deviation? Is this sensor installed in an office environment or a different type of application? Remember that Living Space sensors were designed to be used in applications such as: offices, hotels, school, etc. places where environmental airflow is steady. If this is the case, please open a ticket with the support team so they can investigate the sensor’s performance. Rgds.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore