XPSUAF13AP SAFETY RELAY / RESET AFTER EMERGENCY STOP
  • Industrial Automation
  • XPSUAF13AP SAFETY RELAY / RESET AFTER EMERGENCY STOP
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
Preventa XPS
QUANTUMTECH
QUANTUMTECH
Cadet
Posted: ‎2025-04-30 02:57 AM
947
Dear members ,
We were used to work with the old PREVENTA  safety relays with no issue regarding the Reset/Restart of the rely after an emergency button is pushed ...
However , with this XPSUAF13AP SAFETY RELAY , we are not able to do such an action ,
every time we have to turn OFF & the ON   the relay  in order to restart the system
Would  you please advise your experience with such a product
Thank you in advance
DANY
  • Pushbuttons
Kleber
Ensign Kleber
Ensign
Posted: ‎2025-05-07 04:31 AM
Hello, I use this relay and I have no problem.
I set the START to 7 and FUNCTION to 2.
I use two relays in series, and since I only use the signal from one to reset, I set the START to 7, which is without dynamization.
Instruction sheet: https://download.schneider-electric.com/files?p_enDocType=Instruction+sheet&p_File_Name=PHA71843_08....
QUANTUMTECH
QUANTUMTECH
Cadet
Posted: ‎2025-05-07 11:35 PM
Hello Kleber ,  Thank you for your reply & information