HMIS5T as a slave and M221 as a master on serial Modbus RTU
  • Industrial Automation
  • HMIS5T as a slave and M221 as a master on serial Modbus RTU
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
alpikon
Ensign alpikon
Ensign
Posted: ‎2025-04-27 02:17 AM . Last Modified: ‎2025-04-27 06:03 AM
1332
Hi all,
Looking for advice how to set up HMIS5T as a slave and TM221C16R as a master on serial Modbus RTU.
Required to stop cycle and reset all timers down to 0 on M221 in case lost of serial communication between them.
For now HMIS5T as a master and M221 as a slave runs with no issues,  after serial 485 cable unplugged the cycle executions continue. Was tried setup with Modbus slave RTU driver on HMI and M221 set as slave- no communication.
  • Process Automation Talks
alpikon
Ensign alpikon
Ensign
Posted: ‎2025-05-03 10:53 AM
In response to Bastian_Schmitz
Well, will use your suggestion. Also my initial question still valid.
There screenshot of setup M221 when system frames not received from HMI.
Bastian_Schmitz
Admiral
Posted: ‎2025-05-05 09:48 PM
Your solution seems for me valid.
Replies 5
Bastian_Schmitz
Admiral
Posted: ‎2025-04-29 11:27 PM
1299
I would suggest that you check instead these system words.
I did not test the function, but I would expect you could check in this way if the HMI is not present. Because in that case the number of messages will not change.
alpikon
Ensign alpikon
Ensign
Bastian_Schmitz
Admiral
ismailozinan
Commander ismailozinan Commander
Commander
Posted: ‎2025-05-06 11:09 PM
1231
alpikon
Ensign alpikon
Ensign
Posted: ‎2025-05-08 12:31 AM
In response to ismailozinan
The HMI goes into error if serial unplugged any way. But M221 as a slave continue executing code. To prevent this my solution send M221 to stop all things due to serial communication issue. Physically only one I0.0 has M221 as a emergency stop button, reset of inputs are on HMI side.