Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us enhance search functionality and deliver the results you need faster and more accurately. Click here to take the survey Thank you for helping us build a better Community experience!
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-28 04:59 PM
I found that
The minimum possible motor power rating allowed with any of the ATV61/ATV71 VFD is 0.25 times of VFD's nominal power rating.
For example, ATV71HD30N4 (30KW VFD) ----> The smaller motor rating allowed is 0.25 x 30KW = 7.5KW motor.
Is this the same case for ATV600/ATV900 series drive?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-18 06:37 AM
In fact the limitation will be more on current. The minimum possible motor curent to set will correspond to 0.15 time "In" of the drive name plate (information given on installation manual, depending on your drive). You will then see the equivalent correponding motor power.
To be noted : when using a very small motor it could be necessary to disable the output phase loss protection (OPL) of drive, this avoiding output phase loss detection.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-18 10:50 AM
One other thing to note, when you are using a much smaller motor, the drive may not Auto-Tune. In fact, you may need to erase the Autotune [Autotuning] using [erase Autotuning] and also set the drive [Motor Control Type] Ctt to [U/F VC Quad.] UFq.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-19 04:54 AM
In addition if ATV900 is used, prefer the motor control law uF5 as uFq does exist only on 600.