Hello,
I'm working on ATV320 with an Ethercat Interface board with CHCF set on I-O. When RDY message is displayed I send a controlword with a Forward or Backward command and the inverter starts. StatusWord become UINT#1591. After a while StatusWord changes to UINT#1616, a NST message appear on the display and Inverter stops with statusword UINT#592.
What's going on? Why it doesn't continues to run ?
Thanks to who'll help me!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-02 07:49 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-02 08:21 AM
Thanks for your Replay @Ahmed_Alzafer !
I already read a lot of documentation and FAQs, included which ones you suggested.
All the cases you reported don't include this case unfortunately.
TCC = 2C -> NO
TCC= 3C -> NO
NST is assigned to DI -> NO
Drive is not receiving the proper command signal -> For sure it gets the reset, forward and backward command, if Communication falls could be showed an error?
A loss of a 4-20mA signal is programmed to freewheel stop -> NO
The drive is in terminal control, and the STOP button on the integral or remote keypad was pressed -> NO and I think there is not an STOP button on ATV320 (there is ESC button and small knob to browse the menu).
Any other ideas? How I can see the root of NST message?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-24 08:21 AM
Status Word changing from UINT 1591 to UNIT 1616 and then UINT 592 show the Bit 5 of the status word is changed from 1=> 0.
This means the Quick Stop is active in the drive after the drive reached the desired reference.
The drive performs a fast stop and remains locked in the operating state 6-Quick stop active.
Before restarting the motor, it is required to go to the operating state 2-switch on disabled.
During fast stop, the drive is unlocked and power is supplied to the motor.
The configuration parameters cannot be modified.
The condition for transition 12 to state 2 - Switch on disabled depends on the value of the
parameter Quick stop mode (QStd):
• If the Quick stop mode parameter has the value FST2, the drive stops according to the fast
stop ramp and then changes to state 2 - Switch on disabled .
• If the Quick stop mode parameter has the value FST6, the drive stops according to the fast
stop ramp and then remains in state 6 - Quick stop active until:
◦ A Disable voltage command is received or
◦ The STOP key is pressed or
◦ A freewheel stop command via the digital input of the terminal.